A customer has rented space in a single story building with 3 spaces. Each space has 1600 sq. ft. and is seperated by a lathe and plaster wall. His architect says the seperating walls have a 4 hour fire rating and the space can be wired with romex. Any thoughts on this? thanks bob
|
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
I would check with the AHJ for the area.
ed
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
With the exception of an assembly area, you should be fine with type NM cable.
As NEsaprky said, though, check with the AHJ
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Also keep in mind that if there will be a dropped ceiling, NM cable would not be allowed above the ceiling as open runs.
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
|
Joined: Aug 2002
Posts: 141
OP
Member
|
I called the AHJ and romex it is. No dropped ceiling but thank you for the reminder. bob
|
|
|