#86694 11/20/03 07:34 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
How many of you guys would install GFCI protection for a hard-wired 240 pump motor for in in-ground pool?
I bought a 20-amp 240-volt GFCI breaker for $120.00, and although I am not required to GFCI-protect the pump because it is not fed by a receptacle, I still did.

Money well spent?, or money wasted?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#86695 11/20/03 02:13 PM
Joined: Dec 2002
Posts: 308
E
Member
Doesn't a motor shorten the life of the protecter(GFCI)?

Edward


Thanks
Edward
#86696 11/21/03 11:21 AM
Joined: Sep 2003
Posts: 2
O
OBX Offline
Junior Member
In our area of North Carolina we are required to install GFCI protection for pool pumps, regardless whether plug-in or hardwired.

Tim

#86697 11/21/03 02:47 PM
Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Redsy,

I submitted a proposal for the 2005 NEC to require GFCI protection for all Residential Pool Pumps regardless (or irregardless?) of how they were connected. My reasoning was that many times these pumps are disconnected and reconnected (Season closings, openings & servicing, etc) by less than qualified people and sooner or later will become a hazard. It was shot down.

I've done quite a bit of service work on pools and did referral work from several companies. You'd be surprised what the Owner (or sometimes the 'Pool Guy') will do.

Don't get me started .... [Linked Image]

[Linked Image]
Bill


Bill
#86698 11/21/03 07:01 PM
Joined: Oct 2000
Posts: 5,392
S
Member
I submitted a similar rop also Bill...if only for some rationale, which turned out to be inconclusive.

I also supplied gfi protection for a 3-ph pool motor this year , you may remember the thread...

There would seem to be the bonding camp, as well as the 4-6 ma camp that do not see eye to eye on the issue...

~S~


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,432
Joined: July 2002
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
302,779 Are you busy
231,981 Re: Forum
216,708 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5