The copper water pipe was run over the electrical equipment lower than permitted, but is there a real hazard?

Would you allow this if there were no joints over the area above this equipment?

If so, by what authority?


Joe Tedesco, NEC Consultant
Horizontal Ad
Joined: Apr 2001
Posts: 518
J
Member
I believe that the NEC requires switchboards/switchgear to be in dedicated spaces....
The hazard presented is the risk of condensation forming & then dripping into the gear.
If you're in Reno for the NFPA conference, you might ask the Atlantis casino about the drain they ran over their gear- they blew a breaker that cost them 20K, and a poco transformer as well, darkening part of the town.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Popular Topics(Views)
337,234 Are you busy
262,761 Re: Forum
243,059 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5