#85418 07/02/03 12:18 PM
Joined: Mar 2003
Posts: 849
Y
Member
We have a city utilty building service that feeds 2 water pressure pumps(hydrants & water to homes).They want to add a 75 hp mtr to boost the pressure incase theres a drop in water pressure during a fire. They have refereded to it as a Fire Pump!! So if it trully is a F.P. article 695 comes into play. Heres the questions
#1 Can we put a service rated transfer sw . Run run from the c.t. cabinet to the sevice rated sw. then to normal loads . Also off the load side of the same transfer sw. to the fire pump disconnect then to the fire pump controller?? Since all pumps maintain the city water.
#2 if that is possible could we run straight from the transfer sw. to the fire pump location . With out a dissconnect sw. next to the transfer sw. I take it since they would be considered service wires they
would come under 230-6.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#85419 07/02/03 06:04 PM
Joined: Jun 2001
Posts: 642
N
Member
This does not sound like a true fire pump. Suggest you hook this up as an additional pump system to maintain water pressure in the towns water service.


ed
#85420 07/03/03 10:48 AM
Joined: Mar 2003
Posts: 849
Y
Member
Called Electrical Eng. Explained stutation he reclassed the pump as a booster pump.Poof problem gone.