1 members (Scott35), 201 guests, and 7 robots.
#84440 04/07/03 06:31 PM
I've never seen a 5A circuit breaker.
Better visit England Bill! [Linked Image] Lighting circuits in domestic work are alsmost always 5 or 6A.
I've never seen a normal domestic British dimmer which incorporates fuse protection of its own. Small units are typically rated 250W, and although 5 or 6A circuits are the norm, regulations allow normal lighting outlets to be run on anything up to a 16A branch.
P.S. That's 16A at 240V remember.
[This message has been edited by pauluk (edited 04-07-2003).]
#84441 04/07/03 06:48 PM
Now Paul ....
I'll clarify. Never saw a 5A circuit breaker used as an OCPD in a Panelboard in the US [Linked Image]
Better?
You know I've never seen one anywhere else either. [Linked Image]
#84442 04/07/03 07:12 PM
Bill:
"Small" amperage CB's are used in some control panels. There may still be some listed in the WWGrainger catalog, I haven't looked lately.
#84443 04/07/03 07:35 PM
Ok, I give!! [Linked Image]
I've seen them too used in pieces of individual equipment, but not in a typical residential load center to protect a standard 14 AWG lighting circuit that has 500w or 600w dimmers installed on it.
'Tough room' here sometimes ...
#84444 04/07/03 09:20 PM
This thread has morphed into somthing new, so I'll throw this in
I've seen those modules also. I think their only rated as supplemental protection, and are not aproved for branch circuit protection.
Russ
#84445 04/08/03 08:44 AM
C-H Offline
Threadjack:
The British made MK dimmer switches work like this: (From product sheet)
Approximate load on the Dimmer as a percentage of its maximum rating
Up to 125: Load will receive maximum power continuously.
>125 to 150: Output to load will be reduced to 50% of the maximum after a delay of approximately 20 seconds after switch on.
>150 to 200: Output to load will be reduced to the minimum setting of the dimmer after a delay of approximately 20 seconds after switch on.
>200: Output will be disabled (load will be switched off) almost instantaneously after switch on.
Oh, just in case someone was wondering;
the requirements for dimmers are found in IEC 60669-2-1: Switches for household and similar fixed electrical installations - Part 2-1: Particular requirements - Electronic switches
(Fourth edition, Sept. 2002)
If they sell fifty of them, they'd probably call the title a bestseller. [Linked Image]
[This message has been edited by C-H (edited 04-08-2003).]
#84446 04/13/03 12:30 PM
Z
I follow a simple rule: Nothing under-rates the breaker. 20A Breaker=20A switches=20A outlets=#12 wire or better. I know this rule isn't always adheared to by everybody, but why take a chance when the risk is a fire? On a residential lighting circuit that specs 15A switches, I use a 15A breaker with #14 or better wire. Period. YOu won't be tagged for doing it right...
#84447 04/13/03 03:03 PM
Zapped,
Does that mean you use 1800 watt dimmers on 15 amp breakers and 2400 watt dimmers on 20 amp circuits? [Linked Image]
#84448 04/14/03 01:06 AM
I have a few 5 amp breakers. Made by GE.
I can't read the catalog number on it, but
the breaker is physically the same as a
40 amp GE breaker Catalog number TQC1140.
I also have a Federal Pacific 10A breaker
(not stablok).
