|
1 members (Scott35),
184
guests, and
13
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2003
Posts: 92
OP
Member
|
Is 3 90 degree and 2 offset bends at boxes in 1 run from box to panel code complient? (EMT)
|
|
|
|
Joined: Jan 2003
Posts: 33
Member
|
Per 2002 NEC 358.26 : No more than 360 deg of bends between pull points.
Rich
|
|
|
|
Joined: Jan 2003
Posts: 73
Member
|
Yes, if the offset's do not equal more than 90 degrees.
|
|
|
|
Joined: Mar 2003
Posts: 92
OP
Member
|
Would you consider 2 regular box offsets more than 1 quarter bend?(90 degress)?
|
|
|
|
Joined: Feb 2003
Posts: 138
Member
|
No.
They are typically 10 degrees each for a total of 20. Hence, 90+90+90+20+20=310 total degrees.
[This message has been edited by WebSparky (edited 03-19-2003).]
Dave
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
ok, i'll play..
i've thrown plenty of pvc in dithes that will assume the natural bend of the ditch.
is this 'bent'?
|
|
|
|
Joined: Apr 2001
Posts: 507
Member
|
"is this 'bent'?" Only if the AHJ can see it!
I once had a AHJ do a rough-in inspection. He counted every box offset as a 90° bend. He was the Senior Inspector for the State on Nebraska. He wouldn't listen to reason and it wasn't worth the trouble to go over his head.
Ever since that time I no longer use box offsets on conduit that will get covered with sheetrock.
GJ
|
|
|
|
Joined: Apr 2001
Posts: 449
Member
|
When ever I offset EMT I use 30º bends because it's easy to do the math when the multiplier is 2. That would make my offsets 60º so one of them and 3 90º would still be okay. Your offset would have to use 2 bends greater than 45º to make it a violation and that would be a funky looking offset!
|
|
|
|
Joined: Oct 2002
Posts: 210
Member
|
To me the bends in the ditch is more than just being about passing inspection. To me its a bend because its gonna cause that much more resistance come wire pulling time.
|
|
|
|
Joined: Dec 2001
Posts: 440 Likes: 3
Member
|
You know it's a tough day when an AHJ counts box offsets, and considers "the bend of the ditch" part of the 360 degrees. So I think I would ask him, "If I'm bent over 90 degrees at the waist, does that count also?"
Singing Moon River, Doc
The Watt Doctor Altura Cogen Channelview, TX
|
|
|
Posts: 99
Joined: August 2003
|
|
|
|
|