#84345 03/19/03 05:35 PM
gserve Offline OP
Is 3 90 degree and 2 offset bends at boxes in 1 run from box to panel code complient? (EMT)
#84346 03/19/03 05:53 PM
Per 2002 NEC 358.26 : No more than 360 deg of bends between pull points.
Rich
#84347 03/19/03 05:53 PM
Yes, if the offset's do not equal more than 90 degrees.
#84348 03/19/03 06:35 PM
gserve Offline OP
Would you consider 2 regular box offsets more than 1 quarter bend?(90 degress)?
#84349 03/19/03 06:46 PM
No.
They are typically 10 degrees each for a total of 20. Hence, 90+90+90+20+20=310 total degrees.
[This message has been edited by WebSparky (edited 03-19-2003).]
Dave
#84350 03/19/03 07:11 PM
ok, i'll play..
i've thrown plenty of pvc in dithes that will assume the natural bend of the ditch.
is this 'bent'?
#84351 03/19/03 07:27 PM
"is this 'bent'?"
Only if the AHJ can see it!
I once had a AHJ do a rough-in inspection. He counted every box offset as a 90° bend. He was the Senior Inspector for the State on Nebraska. He wouldn't listen to reason and it wasn't worth the trouble to go over his head.
Ever since that time I no longer use box offsets on conduit that will get covered with sheetrock.
GJ
#84352 03/19/03 07:55 PM
F
When ever I offset EMT I use 30º bends because it's easy to do the math when the multiplier is 2. That would make my offsets 60º so one of them and 3 90º would still be okay. Your offset would have to use 2 bends greater than 45º to make it a violation and that would be a funky looking offset!
#84353 03/23/03 06:24 PM
To me the bends in the ditch is more than just being about passing inspection. To me its a bend because its gonna cause that much more resistance come wire pulling time.
#84354 03/26/03 11:43 PM
You know it's a tough day when an AHJ counts box offsets, and considers "the bend of the ditch" part of the 360 degrees. So I think I would ask him, "If I'm bent over 90 degrees at the waist, does that count also?"
Singing Moon River,
Doc
The Watt Doctor
Altura Cogen