ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
LED retrofit flickers
by rmiell. 01/18/19 08:49 PM
Israel
by Texas_Ranger. 01/14/19 07:12 AM
Free Code class in Maryland 1/16/2019
by Admin. 01/12/19 05:43 PM
Calling all Non-US members!! (Non-US only)
by RODALCO. 01/12/19 02:37 AM
sec cable code conflict
by jake2018. 01/11/19 07:36 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 7 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Accessability #80843
06/04/02 05:34 AM
06/04/02 05:34 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I have a situation where a wall mounted oven is mounted in a base cabinet. The original installer mounted a receptacle behind the oven. But, I don't believe this is accessible as the oven would have to be unscrewed & removed to gain access. They also installed the 120 volt receptacle for the gas cooktop ignition in the same area. I believe that I have to relocate the 120 receptacle and install the j-box for the new hard-wired oven in the back of an adjacent base cabinet, but if I don't have to do so, I would like to leave the wiring intact in order to minimize the cost to these senior citizens.
Any thoughts?

2017 / 2014 NEC & Related Books and Study Guides
Re: Accessability #80844
06/04/02 05:49 AM
06/04/02 05:49 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
The oven setup is ok. The j box can be in the same cabinet as the oven. As for the cooktop I think this is fine. Maybe it would be better if the 120 receptacle was easier accesed but I cant find a code reference that says it must be.

Re: Accessability #80845
06/04/02 07:38 AM
06/04/02 07:38 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
scott,
You think the j-box & receptacle would seem to be "accessible" even though the oven would need to be removed (dismounted) to gain access?
I guess that since no disturbance of the building materials would be required, this may be considered accessible by definition, but I'm not too sure.

Re: Accessability #80846
06/04/02 05:03 PM
06/04/02 05:03 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
the only thing ( other than accessable definitions that i can find...)

Quote
(3) Wall-Mounted Ovens and Counter-Mounted Cooking Units. Wall-mounted ovens and counter-mounted cooking units complete with provisions for mounting and for making electrical connections shall be permitted to be permanently connected or, only for ease in servicing or for installation, cord-and-plug connected.
A separable connector or a plug and receptacle combination in the supply line to an oven or cooking unit shall be approved for the temperature of the space in which it is located.

Re: Accessability #80847
06/04/02 08:54 PM
06/04/02 08:54 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I read that also. I do kitchens everyday and have yet to have an inspector cite me on this type of setup. In a new installation I put the j box in the cabinet above the oven if at all possible. This allows the kitchen guys to install the oven and I dont have to move it to make the connections. Also the only reason you would need to get to the j box would be to disconnect the oven to remove it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
BigB 3
Popular Topics(Views)
252,790 Are you busy
189,600 Re: Forum
179,264 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9674 MB (Peak: 1.1041 MB) Zlib enabled. Server Time: 2019-01-21 18:03:47 UTC