#80828 05/30/02 04:34 PM
Eandrew Offline OP
I'm confused over ampacity adjustments.
Table 310-16 is based on a continuous load without exceeding the insulation temp. rating -article 100
so why is the 80% corretion factor for a continuous load needed? Is this lower ampacity not built into table 310-16?
Is it necessary to lower the normal ampacity in 310-16 by 20% and then size the wire and overcurrent protection to 125% of that value. -Erik
#80829 05/30/02 08:44 PM
Eandrew, article 310-16 is correct. The conductors are rated at 100% and are not the issue in the 80% value. The 80% concerning continuos loads are for OCPD,s and the heat at the connection. If the OCPD is rated for 100% this will not be an issue. I assume by your use of the dash you are refering to the 99 code and if this is the case see 384-16d
Roger
#80830 05/31/02 02:36 AM
Eandrew Offline OP
thanks rodger,
I was thinking that the 80% and 125% related to different things. It is clear to me now. Continuous loads are limited to 80% of the overcurrent device rating. A little algebra and you have an overcurrent device must be at 125% of the continuous load. got it, thanx.
#80831 05/31/02 06:16 PM
You're welcome.
Roger