continuous loads #80828
05/30/02 03:34 PM
05/30/02 03:34 PM
E
Eandrew  Offline OP
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
I'm confused over ampacity adjustments.

Table 310-16 is based on a continuous load without exceeding the insulation temp. rating -article 100

so why is the 80% corretion factor for a continuous load needed? Is this lower ampacity not built into table 310-16?

Is it necessary to lower the normal ampacity in 310-16 by 20% and then size the wire and overcurrent protection to 125% of that value. -Erik

2017 / 2014 NEC & Related Books and Study Guides
Re: continuous loads #80829
05/30/02 07:44 PM
05/30/02 07:44 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Eandrew, article 310-16 is correct. The conductors are rated at 100% and are not the issue in the 80% value. The 80% concerning continuos loads are for OCPD,s and the heat at the connection. If the OCPD is rated for 100% this will not be an issue. I assume by your use of the dash you are refering to the 99 code and if this is the case see 384-16d

Roger

Re: continuous loads #80830
05/31/02 01:36 AM
05/31/02 01:36 AM
E
Eandrew  Offline OP
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
thanks rodger,

I was thinking that the 80% and 125% related to different things. It is clear to me now. Continuous loads are limited to 80% of the overcurrent device rating. A little algebra and you have an overcurrent device must be at 125% of the continuous load. got it, thanx.

Re: continuous loads #80831
05/31/02 05:16 PM
05/31/02 05:16 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
You're welcome.

Roger


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
Popular Topics(Views)
252,848 Are you busy
189,629 Re: Forum
179,302 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.006s) Memory: 0.9586 MB (Peak: 1.0909 MB) Zlib enabled. Server Time: 2019-01-24 10:49:38 UTC