A dedicated EGC run in a separate raceway #80778 05/21/02 08:22 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Hello:

I am installing a new elevator controller on the top of a 23 story building that requires a dedicated equipment grounding conductor that will be run back to the service equipment location. Running this EGC, with the existing phase conductors is not possible without first removing them. The raceway is a 3 inch Rigid Galvanized Steel Conduit, and appears to be a good grounding path with no corrosion, and all fittings are tight.

I have a spare conduit that runs along this conduit that I would like to use.

This appears to be a code violation per Article 250, but I wonder if the CMP is referring to the service conductors, and not to an equipment ground.

I am aware that the impedance of the system may be higher if I do this.

Is this allowable?

Thanks,

Peter Volpe
Electrical Engineer


[This message has been edited by Joe Tedesco (edited 05-21-2002).]


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: A dedicated EGC run in a separate raceway #80779 05/21/02 10:15 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
I haven't seen the 2002 version, but Phillip Simmons' Soares Book on Grounding on the uses and abuses of grounding has been outstanding.

Re: A dedicated EGC run in a separate raceway #80780 05/22/02 06:23 AM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
Peter,
You did not say if the service is a separate service or not. Most elevator rooms I've done are so we will assume this one is also.

You can install an equipment ground in it's own conduit. Yup it raises the impedance WAY high in this case but don't forget, it plays almost no role in fault clearing at any rate, it's only there as a 0 point reference.

My big question is WHY do you need one running all the way back down to, I assume, the building grounding electrode from the 23rd floor? Is there no building steel? In lieu of that, is there no grounding electrode in the closets for xfrmr reference?

If elevator equipment is that sensitive, this stuff is doomed anyway, or are the elevator people becoming like computer people, you know "Our stuff is special".

Good luck.

Re: A dedicated EGC run in a separate raceway #80781 05/22/02 10:43 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
George,
This is an EGC not a grounding electrode conductor and it will carry the fault current. I don't see any exceptions even for an isolated EGC. It is required by 250.134(B) and 300.3(B) to be in the same raceway as the power conductors. If the circuit is above 200 amps or so, the additional inductive reactance of an EGC in a second matallic raceway may very well be high enought so that the OCPD does not open.
Don(resqcapt19)


Don(resqcapt19)
Re: A dedicated EGC run in a separate raceway #80782 05/23/02 10:03 AM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
Don,
OOOOOOPS, I did get that wrong. agreed [Linked Image]

Re: A dedicated EGC run in a separate raceway #80783 05/25/02 12:34 AM
Joined: Oct 2000
Posts: 2,721
Scott35 Online Happy
Broom Pusher and
Member
If this is an IGC [Isolated Grounding Conductor] I think you could run it separate from the Subfeeder or Branch Circuit's Conduit and comply with the NEC.

The "Gurus Of The NEC" have the answers, whereas I only have suggestions and thoughts.

Scott S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: A dedicated EGC run in a separate raceway #80784 05/25/02 09:07 AM
Joined: Apr 2002
Posts: 197
G
Gwz Offline
Member
Scott,

Doesn't 250.146(D) Say " - - - run with the circuit conductors. - - - ." ?

The basic rule of 250.134(B) is not altered by the word " Isolated " of 250.146(D) which is part of 250.146 Section.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,708 Are you busy
204,947 Re: Forum
193,055 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3