Hi Joe,
Not quite as clear as I'd like on my monitor, however...
It looks as though the lower wire is white and has not be re-marked black to indentify it as a hot conductor.
|
|
|
|
|
Joined: Sep 2001
Posts: 25
Member
|
Maybe it's just me, but I don't se a ground to the to the switch either.
|
|
|
|
|
Joined: Apr 2002
Posts: 53
Member
|
Not clear on my monitor and vaguely worded. Does anyone else see if the ground wire is attached to BOTH the box and ground screw on the switch?
|
|
|
|
|
Joined: Apr 2002
Posts: 1
Junior Member
|
Are you talking about the white wire?
The Most Common Mistakes Homeowners Make Doing their Own Wiring... ...as told by an electrician with Over 30 Years Experience (8) Not using the proper replacement outlet is a problem. Always use a GFI receptacle when replacing a kitchen or bathroom receptacle. Also when replacing a garage and outdoor receptacle, use a GFI receptacle. It could save a life- maybe yours, or a loved one.
Wire Sizes, and How to Use Them (6) The two common types of cable used around the home are type NM-B and Type UF. Type NM-B is used inside the home out of the weather in dry areas. Type UF is for use outdoors and underground direct burial cable. Both cables must be protected from damage by running along framing of the home or using conduit where the UF enters the earth and up to four feet where it can be damaged.
210.8(A) & 300.5(D)(1)I thought it was ok say replace with GFCI rec. in these areas, but what about the areas omitted? Where do they come up with the four feet to protect the wiring ?
[This message has been edited by DavidW (edited 04-28-2002).]
David
|
|
|
|
|
Joined: Jan 2002
Posts: 324
Member
|
I see two violations. No grounding conductor which means the metal plate is not grounded (404.9(b)) and white wire is not identified as being other than grounded conductor.
|
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
yeeeeuup, an fer $39.99 youse can git's ya a tooool kit an' be a 'lectricky-an [This message has been edited by sparky (edited 04-28-2002).]
|
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
The title of the section on the other site is "switch replacement". The code requirement to reidentify the white wire in this application first appeared in the '99 code. If the installation was made under prior codes there was no requirement to reisdentify the white. I can't tell for sure if there is a ground wire in the box or not. There is no requirement that the EGC be connected directly to the switch, it is only required to be connected to the metal box. It also could be old enough that 2 wire no ground NM cable was used. The wording on the site makes it clear to reconnect the ground wire if there is one. If there is not an EGC, some additional wording should be added for compliance with the exception to 404.9(B). This would require the use of a nonmetallic face plate when replacing a switch at an outlet without an EGC. Don(resqcapt19)
[This message has been edited by resqcapt19 (edited 04-28-2002).]
Don(resqcapt19)
|
|
|
|
|
Joined: Jan 2001
Posts: 75
Member
|
Is Joe asking about the picture(s) or is he implying something else ?
I rather question the legal part of subscribing.
|
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Looks like most of us saw the same items.
We could beat this thread to death though, but the issue is still one that relates to "existing" versus "new" installations.
I would recommend that the most recent rules be considered, and re-identify the white wire as a hot leg, and use the equipment bonding jumper to the switch, where is is connected to the equipment grounding conductors in the box if any do exist.
That requirement is not new, and has been a requirement in the code for quite a few code cycles, it's the issue about the metal plate that is new.
What happens when something goes wrong with the advice given, and someone gets hurt or there is some property damage?