I am installing fiber optic cables between two buildings. Is there a specific # of pull boxes in a underground PVC conduit run? I was told Every 100' there should be a box. I have a copy of the 1996 NEC handbook and could not find anything.

Thank you,

Shonn Diess


Joe Tedesco, NEC Consultant
Horizontal Ad
Joined: Feb 2001
Posts: 89
E
Member
Looking in my 1999/2002 nec now for relevant (if any) code articles.

Some basic questions:

Have you ever pulled fiber optic cables before ? Have you been trained on how to correctly pull fiber cables ? Fiber cables are easily damaged if not pulled properly.

How long is the run going to end up being ?

Do you require service loops at these 100' intervals ?

The guy pulling the fiber (you) would probably appreciate the JB's every now and then.

Joined: Oct 2000
Posts: 2,749
Member
Shonn:

You should invest in a new copy of the 2002 NECH, I found many rules that apply to the questions you asked, and there are lots of Article 300 rules thay can be applied.


Joe Tedesco, NEC Consultant
Joined: Nov 2000
Posts: 2,148
R
Member
With fiber, you want to reduce the number of times that you have to handle it. Every time you pull it out of a box and loop it to refeed it in, you run additional risk of damage from kinking or other problems. Do a pulling force calculation and make sure that the pulling force required for your pull is less than what is permitted by the manufacturer. As long as the pulling force is within the specs, only place pull points where they are needed for the fiber terminataions. Whenever you use any type of pulling point you have to look at the minimum bending radius permitted for the fiber. In many cases this will require a pull box and not a conduit body.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right
Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Top Posters(30 Days)
Popular Topics(Views)
560,991 Are you busy
434,628 Re: Forum
403,418 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5