ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Where is Everyone?
by luckyshadow - 11/21/21 10:14 AM
It's been an interesting career
by The Watt Doctor - 11/19/21 09:56 AM
Well I am back to stay (nearly 6 years)
by The Watt Doctor - 11/19/21 09:17 AM
Motor Load Relationships Between Fans and Pumps
by The Watt Doctor - 11/18/21 09:24 AM
GFCI's pops in large numbers
by dsk - 11/05/21 06:45 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 32 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,749
Member
I am installing fiber optic cables between two buildings. Is there a specific # of pull boxes in a underground PVC conduit run? I was told Every 100' there should be a box. I have a copy of the 1996 NEC handbook and could not find anything.

Thank you,

Shonn Diess


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Joined: Feb 2001
Posts: 89
E
Member
Looking in my 1999/2002 nec now for relevant (if any) code articles.

Some basic questions:

Have you ever pulled fiber optic cables before ? Have you been trained on how to correctly pull fiber cables ? Fiber cables are easily damaged if not pulled properly.

How long is the run going to end up being ?

Do you require service loops at these 100' intervals ?

The guy pulling the fiber (you) would probably appreciate the JB's every now and then.

Joined: Oct 2000
Posts: 2,749
Member
Shonn:

You should invest in a new copy of the 2002 NECH, I found many rules that apply to the questions you asked, and there are lots of Article 300 rules thay can be applied.


Joe Tedesco, NEC Consultant
Joined: Nov 2000
Posts: 2,148
R
Member
With fiber, you want to reduce the number of times that you have to handle it. Every time you pull it out of a box and loop it to refeed it in, you run additional risk of damage from kinking or other problems. Do a pulling force calculation and make sure that the pulling force required for your pull is less than what is permitted by the manufacturer. As long as the pulling force is within the specs, only place pull points where they are needed for the fiber terminataions. Whenever you use any type of pulling point you have to look at the minimum bending radius permitted for the fiber. In many cases this will require a pull box and not a conduit body.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
286,175 Are you busy
218,629 Re: Forum
204,822 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5