ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#8026 03/05/02 04:45 PM
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
This is not an electrical question - exactly. But, it is a trade question.

I was looking at some new housing construction and found they were converting the black iron pipe stubed into the house to copper water pipe using sweated fittings. IS THIS LEAGLE?

I would not want to be the guy to called to fix a gas leak. Could you emagine putting a torch to a gas pipe?


DB
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
I mean is the LEGAL?


DB
Joined: Nov 2000
Posts: 2,148
R
Member
I don't think that you can do this. I know that sometimes copper is used for the final connection to the equipment, but when it is used, it is connected with flare fittings, not sweated joints. I believe that the odor used in the natural gas to make it easier to detect small leaks is corrosive to copper.
A long time ago when I was in high school, I worked part time at the local hardware store. On a very cold winter day a customer came in and bought a 50' length of garden hose and some adapter fitting from hose thread to pipe thread. As he was going out the door, I just had to ask why garden hose in the winter? His reply, "My hose is cold and I'm going to hook up a gas space heater on the other side of the basement".
Don(resqcapt19)


Don(resqcapt19)
Joined: Jan 2002
Posts: 1,457
E
Member
I am not 100% sure but I beleive that in some parts of the country this is common practice.

Joined: Jan 2002
Posts: 163
D
Member
In the UPC the only approved material for gas is: std. weight wrought iron or steel (galvanized or black), yellow brass (containing not more than 75% copper). Approved PE pipe may be used in exterior buried piping systems. (UPC 1210.1) - I believe similar provisions exist in the IPC

Joined: Apr 2001
Posts: 21
P
Member
In the 2000 edition of UPC, 1210.1 changed to allow Types K, L, and ACR copper. The gas must contain less than 0.3 grains of hydrogen sulfide per ft³ (1210.1.1). The joints must be brazed, flared or screwed (1211.2). So the joints can not be sweated with typical plumbing solder and the code requires the brazer to be certified. Also, there are requirements for labeling, supporting and protecting the copper.

Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
Phil,
The pipe joints did look overheated. Maybe they used a siver solder but it did not look brazed.
Thanks for the input.


DB
Joined: May 2001
Posts: 717
G
Member
Sorry for the delay, see you actually got an answer. The "International Residential Code" section G2413.5.2 says K and L type coppers are allowed, same restriction for Hydroden Sulfide. G2413.10.2 says joints are made with an approved gas type fitting or brazed, that's where your 'overheated' type joint would come from.

Let's face it guys, were talking about 3 lbs max here, the only real worry is probably piercing the pipe with something.

Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
Thanks for clearing it up. Guess it is legal and safe. It just seems unsafe or least unwise considering the homeowner may decide to try to fix or modify a line himself.

I could also see a ice maker installer tapping the gas line thinking it is a water line.