Natural Gas thru Copper Pipe #8026 03/05/02 04:45 PM
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
This is not an electrical question - exactly. But, it is a trade question.

I was looking at some new housing construction and found they were converting the black iron pipe stubed into the house to copper water pipe using sweated fittings. IS THIS LEAGLE?

I would not want to be the guy to called to fix a gas leak. Could you emagine putting a torch to a gas pipe?


DB
Work Gear for Electricians and the Trades
Re: Natural Gas thru Copper Pipe #8027 03/05/02 05:26 PM
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
I mean is the LEGAL?


DB
Re: Natural Gas thru Copper Pipe #8028 03/05/02 05:42 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
I don't think that you can do this. I know that sometimes copper is used for the final connection to the equipment, but when it is used, it is connected with flare fittings, not sweated joints. I believe that the odor used in the natural gas to make it easier to detect small leaks is corrosive to copper.
A long time ago when I was in high school, I worked part time at the local hardware store. On a very cold winter day a customer came in and bought a 50' length of garden hose and some adapter fitting from hose thread to pipe thread. As he was going out the door, I just had to ask why garden hose in the winter? His reply, "My hose is cold and I'm going to hook up a gas space heater on the other side of the basement".
Don(resqcapt19)


Don(resqcapt19)
Re: Natural Gas thru Copper Pipe #8029 03/05/02 06:48 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
I am not 100% sure but I beleive that in some parts of the country this is common practice.

Re: Natural Gas thru Copper Pipe #8030 03/06/02 03:33 PM
Joined: Jan 2002
Posts: 163
D
dana1028 Offline
Member
In the UPC the only approved material for gas is: std. weight wrought iron or steel (galvanized or black), yellow brass (containing not more than 75% copper). Approved PE pipe may be used in exterior buried piping systems. (UPC 1210.1) - I believe similar provisions exist in the IPC

Re: Natural Gas thru Copper Pipe #8031 03/09/02 06:06 PM
Joined: Apr 2001
Posts: 21
P
Phil H Offline
Member
In the 2000 edition of UPC, 1210.1 changed to allow Types K, L, and ACR copper. The gas must contain less than 0.3 grains of hydrogen sulfide per ft³ (1210.1.1). The joints must be brazed, flared or screwed (1211.2). So the joints can not be sweated with typical plumbing solder and the code requires the brazer to be certified. Also, there are requirements for labeling, supporting and protecting the copper.

Re: Natural Gas thru Copper Pipe #8032 03/09/02 09:08 PM
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
Phil,
The pipe joints did look overheated. Maybe they used a siver solder but it did not look brazed.
Thanks for the input.


DB
Re: Natural Gas thru Copper Pipe #8033 03/10/02 02:13 PM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
Sorry for the delay, see you actually got an answer. The "International Residential Code" section G2413.5.2 says K and L type coppers are allowed, same restriction for Hydroden Sulfide. G2413.10.2 says joints are made with an approved gas type fitting or brazed, that's where your 'overheated' type joint would come from.

Let's face it guys, were talking about 3 lbs max here, the only real worry is probably piercing the pipe with something.

Re: Natural Gas thru Copper Pipe #8034 03/11/02 02:56 PM
Joined: Mar 2002
Posts: 18
D
DB Offline OP
Member
Thanks for clearing it up. Guess it is legal and safe. It just seems unsafe or least unwise considering the homeowner may decide to try to fix or modify a line himself.

I could also see a ice maker installer tapping the gas line thinking it is a water line.


DB

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3