Transfer switches #79991 02/12/02 08:35 PM
Joined: Feb 2002
Posts: 6
C
cthusky Offline OP
Junior Member
When installing a transfer switch ahead of a main breaker panel,should you bring all available grounding electrode conductors to the transfer switch (listed as suitable for use as service equipment, therefore considered first point of disconect?)and bond right there, then use SER from the transfer switch to the panel? Or is SEU o.k to use from the transfer switch to the panel,considering the panel is usally only a foot or two away??

2017 / 2014 NEC & Related Books and Study Guides
Re: Transfer switches #79992 02/12/02 08:38 PM
Joined: Jul 2001
Posts: 29
T
tmon Offline
Member
Does the transferswitch have a disconnecting means or overcurrent protective device built in?

Re: Transfer switches #79993 02/12/02 08:47 PM
Joined: Feb 2002
Posts: 6
C
cthusky Offline OP
Junior Member
I believe the actual transfer switch is the disconnect. It is labeled as suitable for use as service equipment. It does not contain overcurrent protection though.

[This message has been edited by cthusky (edited 02-12-2002).]

Re: Transfer switches #79994 02/14/02 11:12 AM
Joined: Jan 2002
Posts: 21
M
MVillines Offline
Member
Cthusky
I’ll try to keep this as short as possible. First look at Service-Equipment in the definitions then section 230.91(NEC 2002) allows the service disconnect to be located immediately adjacent to the overcurrent device (main breaker). Both the transfer switch and the distribution panel are considered service-equipment. 250.24(C) specifies that the grounding electrode conductor be connected to the service-equipment, that could be either the transfer switch or the distribution panel adjacent to the transfer switch, both are consider service-equipment. Either place you land the grounding electrode conductor, only three conductors between the transfer switch and the dist panel is all that is required between the two panels using the Edison three-wire system.

Re: Transfer switches #79995 02/17/02 01:35 PM
Joined: Feb 2002
Posts: 6
C
cthusky Offline OP
Junior Member
Thanks for the reply,I thought though you needed to use SER because of 250-24(a)(5). Since the transfer switch is the bonding point/disconnecting means, using a three wire to the panel from there would mean a "load side connection" of the grounded and grounding conductors.Yes/no


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,026 Are you busy
205,035 Re: Forum
193,143 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3