0 members (), 458 guests, and 24 robots.
#78828 10/27/01 05:21 PM
sparky Offline OP
Yup its 440.65. not 440-65, reminds me of star trek ( star date 440.65...) [Linked Image]
ok, lemme read this to you here...
Single-Phase cord & plug connected room air conditioners shall be provided with factory-installed LCDI or AFCI protection. The LCDI or AFCI protection shall be an integral part of the attacthment plug or be located in the power supply cord within 300 mm (12 in) of the attatchment plug.
What is a LCDI ?
Has anyone seen one in breaker form?
What if the circuit already has AFCI protection?
Would this take the place of AFCI protection in a bedroom dedicated AC circuit?
What next, AFCI for dryer circuits to address static cling?
I,m soooo [Linked Image]
#78829 10/27/01 08:03 PM
Sparky,
Haven't heard that one yet!
I don't have the '02 yet (next week) but I did download the drafts in PDF from NFPA - guess what?
There is no 440.65 there! maybe it was a last minute addition? [Linked Image]
#78830 10/27/01 09:46 PM
F
Leakage Current Detection and Interruption (LCDI) and no, I don't know either.
#78831 10/28/01 08:08 AM
NEC 2002 440.65 notes the AFCI or LCDI to be an integral part of the attachment plug or within 12" of the attachment plug.
That leaves the branch circuit portion to the recp out of the picture.
#78832 10/29/01 04:44 PM
Bill and Sparky
LCDI 'leakage current detection and interruption.
and that is 440.65, now is that not what a GFCI does. they are turning a once great trade into a bunch of Sea-lawyers.
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
555,808 Are you busy
430,644 Re: Forum
400,006 Need opinion