ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
240V only in a home and NEC?
by Hutch - 05/13/24 04:23 PM
Electricians revenge
by gfretwell - 05/09/24 08:24 PM
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 210 guests, and 6 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#77941 07/24/01 05:17 PM
Joined: May 2001
Posts: 17
H
habbbby Offline OP
Member
Is it permissable to make splices in a service enterance JB? To run conduit to JB and from JB and make the splice next to enterance cables that arent protected?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#77942 07/24/01 05:27 PM
A
Anonymous
Unregistered
I can't quite picture what you want to do. [Linked Image]

Are you running a cable past your service equipment and you want it to just pass through your SE so you can splice it?

I don't like idea that at all.

#77943 07/24/01 05:35 PM
Joined: May 2001
Posts: 17
H
habbbby Offline OP
Member
Actually, Iam not doing it but might be asked to continue the job. Conduit was ran from the SE to a light pole, inexperience to blame on this one, instead of running it from light pole to dwelling. Now they want to run conduit from SE to dwelling and make the splice in the SE.

#77944 07/25/01 12:00 PM
Joined: May 2001
Posts: 176
W
Member
Like Dspark, I am having some difficulty in getting the picture of your application. Sounds like your Service Entrance is coming out of a Utility transformer underground to a light pole, possibly for a light fixture. Now you want to tap the SE, and continue to a dwelling. Taking the liberty to make these assumptions, i think the tap would want to be the same size as the SE, assuming it is properly sized. If it is SE cable per Art. 338, then the box may need resizing due to the bend requirements. Then the splice will have to be properly done in accordance with Art 110-14.
The best way would be as you suggested, a continuous SE from Utility to dwelling, then to feed the light from there.

#77945 07/25/01 01:30 PM
Joined: May 2001
Posts: 17
H
habbbby Offline OP
Member
Well, the service equipment was already in place, they just installed another disco,etc, and ran conduit from there, underground to new dwelling. Then they ran a conduit from the SE to a light pole that will have a dusk to dawn. It should have been run from the pole to the dwelling. My question is, can the conductors run through the JB at SE, and then be ran to the dwelling to the dist. panel? AWG 12's were pulled and are bundled in the SE, to splice and continue on to the dwelling in a seperate conduit from the service. Follow me?

#77946 07/25/01 06:39 PM
Joined: Oct 2000
Posts: 5,392
S
Member
i think so habbbby;

230-46 says ok to splice it.
230-7 gotta be in it's own pipe.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5