#77246 05/16/01 04:06 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
can you run a 3/4" conduit into a 1 1/2" tee from each entry or do you have to exit the fitting using trade size conduit that is equal to the fitting size?

i beleive that the conduits exiting the fitting must be the same trade size as the fitting then you can reduce using a coupling and an re or a bell end reducer...

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#77247 05/16/01 04:22 PM
Joined: Nov 2000
Posts: 2,148
R
Member
The code issue here is the support of the fitting. Look at 370-23(e) Exception. If you support the 1 1/2" T independently of the 3/4" conduit it would be ok. If the 3/4" conduit is supporting the 1 1/2" T it is a violation.

Don(resqcapt19)


Don(resqcapt19)
#77248 05/18/01 07:03 PM
Joined: Nov 2000
Posts: 2,148
R
Member
I have changed my mind. If the volume of the conduit body is 100 cu. in. or less, then any size conduit would be permitted to support the fitting.
Don(resqcapt19)


Don(resqcapt19)
#77249 05/18/01 09:07 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
Quote
Originally posted by resqcapt19:
I have changed my mind. If the volume of the conduit body is 100 cu. in. or less, then any size conduit would be permitted to support the fitting.
Don(resqcapt19)


as i read it, this is not referring to a TEE or an LB. it is referring to an enclosure. i think this should be addressed as a "conduit body" as defined in article 100.

#77250 05/19/01 01:29 AM
Joined: Nov 2000
Posts: 2,148
R
Member
The fact that the exception to 370-23(e) specifies conduit bodies makes me say that the section itself includes conduit bodies of 100 cu. in. or less. If the section did not include conduit bodies, there would be no reason to have the exception.
Don(resqcapt19)


Don(resqcapt19)
#77251 05/19/01 08:19 AM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
Quote
Originally posted by resqcapt19:
The fact that the exception to 370-23(e) specifies conduit bodies makes me say that the section itself includes conduit bodies of 100 cu. in. or less. If the section did not include conduit bodies, there would be no reason to have the exception.
Don(resqcapt19)

i will have to agree with you on this one. while working in alaska in 1996 the state inspector gigged us on a lot of the same situations hence my assumption that the situation was not allowed.

the 100cu inch is what saves the whole thing to me. i still think it looks bad...i can see the benefit of doing this on lighting runs but it looks terrible.

thanks for the replies

#77252 08/06/01 09:39 AM
Joined: Mar 2001
Posts: 345
T
Member
Quote
Originally posted by frodo:
Can you run a 3/4" conduit into a 1 1/2" tee from each entry or do you have to exit the fitting using trade size conduit that is equal to the fitting size?

I belive that the conduits exiting the fitting must be the same trade size as the fitting then you can reduce using a coupling and an re or a bell end reducer...

Why on earth would anyone want us to put the RE anywhere except the fitting itself. Having the RE as close to the opening in the fitting as practicable will facilitate fishing and pulling the attached raceways.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard