Article 370-23 (e) (f) #77246
05/16/01 04:06 PM
05/16/01 04:06 PM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
can you run a 3/4" conduit into a 1 1/2" tee from each entry or do you have to exit the fitting using trade size conduit that is equal to the fitting size?

i beleive that the conduits exiting the fitting must be the same trade size as the fitting then you can reduce using a coupling and an re or a bell end reducer...

2017 / 2014 NEC & Related Books and Study Guides
Re: Article 370-23 (e) (f) #77247
05/16/01 04:22 PM
05/16/01 04:22 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The code issue here is the support of the fitting. Look at 370-23(e) Exception. If you support the 1 1/2" T independently of the 3/4" conduit it would be ok. If the 3/4" conduit is supporting the 1 1/2" T it is a violation.

Don(resqcapt19)


Don(resqcapt19)
Re: Article 370-23 (e) (f) #77248
05/18/01 07:03 PM
05/18/01 07:03 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I have changed my mind. If the volume of the conduit body is 100 cu. in. or less, then any size conduit would be permitted to support the fitting.
Don(resqcapt19)


Don(resqcapt19)
Re: Article 370-23 (e) (f) #77249
05/18/01 09:07 PM
05/18/01 09:07 PM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
Quote
Originally posted by resqcapt19:
I have changed my mind. If the volume of the conduit body is 100 cu. in. or less, then any size conduit would be permitted to support the fitting.
Don(resqcapt19)



as i read it, this is not referring to a TEE or an LB. it is referring to an enclosure. i think this should be addressed as a "conduit body" as defined in article 100.

Re: Article 370-23 (e) (f) #77250
05/19/01 01:29 AM
05/19/01 01:29 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The fact that the exception to 370-23(e) specifies conduit bodies makes me say that the section itself includes conduit bodies of 100 cu. in. or less. If the section did not include conduit bodies, there would be no reason to have the exception.
Don(resqcapt19)


Don(resqcapt19)
Re: Article 370-23 (e) (f) #77251
05/19/01 08:19 AM
05/19/01 08:19 AM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
Quote
Originally posted by resqcapt19:
The fact that the exception to 370-23(e) specifies conduit bodies makes me say that the section itself includes conduit bodies of 100 cu. in. or less. If the section did not include conduit bodies, there would be no reason to have the exception.
Don(resqcapt19)


i will have to agree with you on this one. while working in alaska in 1996 the state inspector gigged us on a lot of the same situations hence my assumption that the situation was not allowed.

the 100cu inch is what saves the whole thing to me. i still think it looks bad...i can see the benefit of doing this on lighting runs but it looks terrible.

thanks for the replies

Re: Article 370-23 (e) (f) #77252
08/06/01 09:39 AM
08/06/01 09:39 AM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
Quote
Originally posted by frodo:
Can you run a 3/4" conduit into a 1 1/2" tee from each entry or do you have to exit the fitting using trade size conduit that is equal to the fitting size?

I belive that the conduits exiting the fitting must be the same trade size as the fitting then you can reduce using a coupling and an re or a bell end reducer...


Why on earth would anyone want us to put the RE anywhere except the fitting itself. Having the RE as close to the opening in the fitting as practicable will facilitate fishing and pulling the attached raceways.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 11
Popular Topics(Views)
249,267 Are you busy
187,199 Re: Forum
176,554 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9847 MB (Peak: 1.1373 MB) Zlib enabled. Server Time: 2018-09-18 23:39:55 UTC