1 members (Scott35),
216
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2000
Posts: 84
OP
Member
|
Most generators I've seen have an integral circuit breaker. I'll give the following example. A 50KW 120/208V. 3 phase 4/W. The generator would be the only power source to feed a panelboard 50 feet away that will be used in a Park setting for a special event. I would ground and bond at the generator and isolate the neutral in the "remote" panelboard. My feeder assembly would consist of (three) phase conductors, a neutral conductor and an equipment grounding conductor. Does anybody disagree with this installation?
Frank (cinkerf)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
So, the generators main would be the main disco, within sight? the panelboard in MLO?? [This message has been edited by sparky (edited 04-19-2001).]
|
|
|
|
Joined: Dec 2000
Posts: 84
OP
Member
|
Sparky,
I would probably have a main disconnect in the remote panelboard. Grounding is the real point of my question. If the generator has a main circuit breaker then anything downstream of it should be treated as a feeder. At least that is my understanding. I'm just interested in how other people around the country view this and how they ground such an installation.
Frank (cinkerf)
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Frank, Sounds good to me. Bill
Bill
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
At the risk of having my opinion rammed down my throat. I will state: you don't need the EGC if you use a non-metallic jacketed multi-conductor cable from the generator to the remote panel and there are no continuous metallic paths (e.g., metal conduit/flex) bonded to the grounding system at the generator and panelboard (no parallel path back to the generator). You ensure the generator frame is bonded to its grounded conductor. Drive a ground rod near the generator and connect the GEC to the generator's grounded conductor. Treat the remote panel as a service panel. Bond the panelboard and EGC buss to the neutral. Drive a ground rod and install a GEC connected to the neutral in the panelboard. Or you could do it just the way you described it. Thanks
|
|
|
|
Joined: Dec 2000
Posts: 84
OP
Member
|
Mike,
I have seen it done that way. I guess that is why I raised the question in the first place. I wasn't aware that both were acceptable methods. The integral generator circuit breaker is what made me post the question.
Frank (cinkerf)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Mike; i'm not going to disagree, as either method could be NEC justified. But i would like to have some fun with it! what say we do it that way, and the genny's only 20' away.....real low impedance soil.....somebody must have had a garden or chickenhouse there at one time......
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Sparky, Sounds like a good place to open a Bait Stand! Bill
Bill
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
Good question, Sparky! Are you suggesting the possibility of a parallel path with the ground rods 20 feet apart? The NEC states that a ground rod must have a 25 ohm or less impedance. A second ground rod is required if the first one is more than 25 ohms. Also, the GEC/rod and grounded conductor are the same potential. And the grounded conductor has the least resistance.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Mike; well yes, and apparently code compliant too, jsut fishin' for opinion, beats cuttin' bait!
|
|
|
Posts: 5,445
Joined: January 2005
|
|
|
|
|