Hi all,
I have to install outlets in the basement, the studs are 1.5" thick and the insulation is 1.5", the drywall is .5" ,this gives me at least 2" clearance from the concrete wall. If I put the NM B wires in between stud and insulation will this be up to CODE ? I'm thinking that that any 1.25" screw or nail can't reach the wire so this will be OK. I just don't want to remove the insulation and use conduit (?).
Thanks,
Arthur
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
You can notch the front side of the studs and lay the romex in there and install metal nail plates over the romex. Keep the romex no less than 1 1/4" from the front of the studs for the vertical run(s) of romex to the outlet boxes (running parallel to the studs).
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
Correction; steel nail plate a minimum of 1/16" thick.
|
|
|
|
Joined: Oct 2000
Posts: 4,155 Likes: 5
Member
|
Arthur, I'm having a hard time picturing what you are talking about. Are these studs 'on the Flat' against the concrete wall? What type of insulation? I'm trying to figure out what you mean by going between the stud and insulation. the studs are 1.5" thick and the insulation is 1.5", the drywall is .5" ,this gives me at least 2" clearance from the concrete wall. If I put the NM B wires in between stud and insulation will this be up to CODE ? Bill
Bill
|
|
|
|
Joined: Mar 2001
Posts: 3
OP
Junior Member
|
The studs and the rigid insulation were already in placed by the builder. Shall I say 'can I put the wires in the gap between the stud and insulation' ? or simply at the side of the stud adjacent to the insulation ? Thanks, Arthur Originally posted by Bill Addiss: Arthur,
I'm having a hard time picturing what you are talking about. Are these studs 'on the Flat' against the concrete wall? What type of insulation? I'm trying to figure out what you mean by going between the stud and insulation.
Bill
|
|
|
|
Joined: Oct 2000
Posts: 4,155 Likes: 5
Member
|
Arthur,
You should be Ok if you can figure some way of securing the cable back there (all the way).
Make sure that you are using boxes of the proper cu. in. capacity.
Bill