I have a customer that wants to rewire her 1800 square foot residence because of aluminum wiring and I was told that the only "approved" method now was the COPALUM crimp method. So I went online and looked at this method and thought it does not look that bad. UNTIL I called for pricing. COPALUM makes you get certified through them ONLY! $750 for up to six people and you have to pick up the Air Fare, meals, rental car, and hotel. Or you can go to them for $350. Then you can lease the crimp $1000 for the first 3mo and then $290 mo after that. The crimps are $460-600 for 200 pcs and 200 pcs heat shrink. What ever happend to using a #65 Ideal Purple Wire nut?
|
|
|
|
Joined: May 2003
Posts: 1,157
Member
|
Because they burn up might be the reason . I have seen quite a few pics with burned purple wirenuts.
And yeah thats nothing new about the AMP product . Al wiring I usually turn those jobs down because of liability issues better off to rewire in copper.
|
|
|
|
Joined: Jan 2003
Posts: 1,429
Member
|
"What ever happend to using a #65 Ideal Purple Wire nut?" From reading the manufacture instructions, it states the #65 Purple is only for temp. connections. The new King connectors are approved, and are not that expensive. http://www.kinginnovation.com/
|
|
|
|
Joined: Dec 2000
Posts: 4,293
Member
|
I'll second the use of the Alumi-Con connectors from King. I've used them and like them.
If you use a torque screwdriver and the spec provided with them, they are listed.
|
|
|
|
Joined: May 2006
Posts: 17
Junior Member
|
I read in a wiring book that you can use Madison brand split bolt connectors to splice aluminum to copper. Be sure to use anti corrosion paste on the aluminum wire too.
Aaron
|
|
|
Posts: 806
Joined: October 2004
|
|
|
|
|