#75632 - 03/06/07 06:44 PM interlocking disconnects  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
Can anyone spec a disonnect with door interlock that also breaks the load via a contactor? Supply is three phase, 208 volt up to 600 volt, 100 to 200 amps. I am looking at a device that will prevent unauthorized persons from using the disconnect to break the load , and prevent them from opening an energized disconnect. thanks.


Work Gear for Electricians and the Trades

#75633 - 03/06/07 08:54 PM Re: interlocking disconnects  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Jay,
You can get field installed control circuit interlock switches for most disconnects. These interlock switches open before the main contacts of the disconnect and could be used to control a remote contactor.
Don


Don(resqcapt19)


Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7437 MB (Peak: 0.8598 MB) Zlib enabled. Server Time: 2017-10-22 13:26:12 UTC