interlocking disconnects #75632
03/06/07 05:44 PM
03/06/07 05:44 PM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
Can anyone spec a disonnect with door interlock that also breaks the load via a contactor? Supply is three phase, 208 volt up to 600 volt, 100 to 200 amps. I am looking at a device that will prevent unauthorized persons from using the disconnect to break the load , and prevent them from opening an energized disconnect. thanks.

Work Gear for Electricians and the Trades
Re: interlocking disconnects #75633
03/06/07 07:54 PM
03/06/07 07:54 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Jay,
You can get field installed control circuit interlock switches for most disconnects. These interlock switches open before the main contacts of the disconnect and could be used to control a remote contactor.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,230 Are you busy
189,198 Re: Forum
178,881 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9425 MB (Peak: 1.0602 MB) Zlib enabled. Server Time: 2018-12-16 04:23:30 UTC