Posted By: jay8 interlocking disconnects - 03/06/07 10:44 PM
Can anyone spec a disonnect with door interlock that also breaks the load via a contactor? Supply is three phase, 208 volt up to 600 volt, 100 to 200 amps. I am looking at a device that will prevent unauthorized persons from using the disconnect to break the load , and prevent them from opening an energized disconnect. thanks.
Posted By: resqcapt19 Re: interlocking disconnects - 03/07/07 12:54 AM
Jay,
You can get field installed control circuit interlock switches for most disconnects. These interlock switches open before the main contacts of the disconnect and could be used to control a remote contactor.
Don