If you are derating wire due to conduit fill(example - 4/0 derated to 3/0 ampacity) should the circuit breaker be sized to protect the new derated amapacity of the 4/0?

Joined: Feb 2003
Posts: 231
R
Member
No, stay with circuit breaker size and just increase the awg of the wire when you have to derate.




[This message has been edited by RobbieD (edited 02-17-2007).]

Joined: Mar 2005
Posts: 1,213
S
Member
The derated ampacity cannot exceed the overcurrent protection. So, you either have to downsize the breaker or upsize the cable. Normally, it's the latter since the original breaker size is chosen for a reason, but using a smaller breaker is OK if circumstances allow.

Joined: May 2005
Posts: 984
Likes: 1
G
Member
Huh?
Are you saying that I can't feed a 15 amp load with a 20 amp breaker using #8 wire???