208V questions #7470 02/06/02 07:57 PM
Joined: Dec 2000
Posts: 45
D
dugmaze Offline OP
Member
My neighbor has three new baseboard heaters and wanted me to install them. They are 208V and I told him that they cannot be used. From my understanding, 208V is 220V three-phase to ground.

Am I correct?

Thanks in advance, Doug.

Work Gear for Electricians and the Trades
Re: 208V questions #7471 02/06/02 08:18 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Doug,
Are you sure that they are not dual rated 208/240? Most of them that I have seen are. The wattage is 25% less when on 208.
Don(resqcapt19)


Don(resqcapt19)
Re: 208V questions #7472 02/06/02 11:00 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
The 208 that you refer to is the "high-leg" voltage to ground on a 240/120 volt 3 phase delta connected transformer secondary with on of the windings tapped at midpoint to provide 120 volts. The voltage of one of the phases, usually the "B" phase is about 208 and obviously should be avoided if connecting 120 volt equipment.
There is also a wye connected 208/120 3 phase system where all 3 phases are at 120 volts to ground.

Re: 208V questions #7473 02/06/02 11:37 PM
Joined: Dec 2000
Posts: 45
D
dugmaze Offline OP
Member
No, I double checked and it is only 208V. So if all I have is 120V single phase or 220V two phase then I can't wire this up.

Re: 208V questions #7474 02/07/02 08:04 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
I would not use 208 heaters at 240 volt. But, most of the ones I've seen are dual rated. If they are not dual rated, have him get 240 volt heaters.
BTW, you probably do not have two-phase voltage. It is very uncommon these days. You must mean 240 volt single phase with a neutral. This is the standard residential system.

Re: 208V questions #7475 02/07/02 09:21 AM
Joined: Feb 2002
Posts: 11
B
bobc Offline
Member
Doug,

Three phase 208 is derived from a four wire

wye connected transformer configuration .

120 volts to neutral,208 phase to phase

Re: 208V questions #7476 02/07/02 11:00 AM
Joined: Dec 2000
Posts: 45
D
dugmaze Offline OP
Member
Somebody must have bought these for a commercial building. Thanks for your help.

Re: 208V questions #7477 02/07/02 08:02 PM
Joined: Aug 2001
Posts: 329
S
Steve Miller Offline
Member
Doing a little basic Ohm's Law here (ignoring the fact that this is AC not DC) you'll find that a 5000 watt (I just used this value for comparison) 208v unit draws 24 amps and has ~8.67 Ohms resistance. The same unit at 240v would draw ~28 amps and put out 6720 watts (R basically stays the same). Their life span will be real short.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,911 Are you busy
204,345 Re: Forum
192,566 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3