Transfer switch #74650 01/30/07 06:38 AM
Joined: Jan 2007
Posts: 12
G
guschash Offline OP
Member
I will doing my first residentical transfer switch hook-up. Do I tie the neutrals together at the transfer switch enclosure.

[This message has been edited by guschash (edited 01-30-2007).]

Work Gear for Electricians and the Trades
Re: Transfer switch #74651 01/30/07 07:05 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
Yes. There needs to be exactly one ground/neutral connection in the entire system, and the ATS is generally the place to do it. (250.30(A)(1) Exception 1 permits this.

NEC 250.30 will tell you what you need to know. Well, if you can decipher it at least- it's one of the most confusing codes to try to read. Why can't the NEC just use plain english?

[This message has been edited by SteveFehr (edited 01-30-2007).]

Re: Transfer switch #74652 01/30/07 10:15 AM
Joined: Jun 2005
Posts: 821
S
ShockMe77 Offline
Member
I haven't done many of these but the ones I have done have NOT been seperately dervied systems since the grounded conductor was NOT switched.

Re: Transfer switch #74653 01/30/07 06:31 PM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
It was my understanding that generators and UPSs are are always a seperately derived source, regardless of how the neutral is handled.

Quoth NEC 2005:
Quote
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.

Quote
250.30(A)(1) Exception No.1: For separately derived systems that are dual fed (double ended) in a common enclosure or grouped together in separate enclosures and employing a secondary tie, a single system bonding jumper connection to the tie point of the grounded circuit conductors from each power source shall be permitted

[This message has been edited by SteveFehr (edited 01-30-2007).]

Re: Transfer switch #74654 01/30/07 06:54 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
It is up to the installer to decide if it will be a separately derived system or not.

If you switch the neutral and put a bonding jumper at the generator it will be an SDS.

If you do not switch the neutral and do not install a bonding jumper at the generator than it will not be an SDS.

Both ways have advantages and disadvantages.

Primarily non-SDS is cheaper, SDS works better with GFP mains.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Transfer switch #74655 01/30/07 07:02 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
You also need to check the generator. Some come with the neutral bonded, others, particularly Honda, don't.


Greg Fretwell
Re: Transfer switch #74656 01/31/07 06:24 AM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
Interesting that you mention Honda, with this being a foreign make. By far the majority of generators on the U.K. market are sold with an unbonded neutral, as I believe are most in Europe. Perhaps this accounts for it?

Re: Transfer switch #74657 01/31/07 06:57 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
That's odd, now that you mention it- I'd think it would be the other way around, as PME & shared earth/neutral is illegal in the US but more prevalent in Europe.

Boy that THAT throw me for a loop the first time I saw it! 3W WYE bus duct? Not very common in the US [Linked Image]

[This message has been edited by SteveFehr (edited 01-31-2007).]

Re: Transfer switch #74658 01/31/07 06:30 PM
Joined: Jan 2007
Posts: 12
G
guschash Offline OP
Member
This is a Honda, so if I don't tie neutrals together, how do the loads that will be running now on the generator get there neutal. From the generator?

Re: Transfer switch #74659 01/31/07 07:57 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Guschash, here is a diagram from Ed MacLaren that shows a proper hook up for an unswitched neutral transfer switch.

Notice the generator neutral is not bonded to the generator housing.

[Linked Image]

Roger

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,205 Are you busy
206,090 Re: Forum
194,093 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3