Transfer switch #74650
01/30/07 06:38 AM
01/30/07 06:38 AM
G
guschash  Offline OP
Member
Joined: Jan 2007
Posts: 12
Walbridge,Ohio,wood
I will doing my first residentical transfer switch hook-up. Do I tie the neutrals together at the transfer switch enclosure.

[This message has been edited by guschash (edited 01-30-2007).]

Work Gear for Electricians and the Trades
Re: Transfer switch #74651
01/30/07 07:05 AM
01/30/07 07:05 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Yes. There needs to be exactly one ground/neutral connection in the entire system, and the ATS is generally the place to do it. (250.30(A)(1) Exception 1 permits this.

NEC 250.30 will tell you what you need to know. Well, if you can decipher it at least- it's one of the most confusing codes to try to read. Why can't the NEC just use plain english?

[This message has been edited by SteveFehr (edited 01-30-2007).]

Re: Transfer switch #74652
01/30/07 10:15 AM
01/30/07 10:15 AM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I haven't done many of these but the ones I have done have NOT been seperately dervied systems since the grounded conductor was NOT switched.

Re: Transfer switch #74653
01/30/07 06:31 PM
01/30/07 06:31 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
It was my understanding that generators and UPSs are are always a seperately derived source, regardless of how the neutral is handled.

Quoth NEC 2005:
Quote
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.


Quote
250.30(A)(1) Exception No.1: For separately derived systems that are dual fed (double ended) in a common enclosure or grouped together in separate enclosures and employing a secondary tie, a single system bonding jumper connection to the tie point of the grounded circuit conductors from each power source shall be permitted


[This message has been edited by SteveFehr (edited 01-30-2007).]

Re: Transfer switch #74654
01/30/07 06:54 PM
01/30/07 06:54 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
It is up to the installer to decide if it will be a separately derived system or not.

If you switch the neutral and put a bonding jumper at the generator it will be an SDS.

If you do not switch the neutral and do not install a bonding jumper at the generator than it will not be an SDS.

Both ways have advantages and disadvantages.

Primarily non-SDS is cheaper, SDS works better with GFP mains.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Transfer switch #74655
01/30/07 07:02 PM
01/30/07 07:02 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
You also need to check the generator. Some come with the neutral bonded, others, particularly Honda, don't.


Greg Fretwell
Re: Transfer switch #74656
01/31/07 06:24 AM
01/31/07 06:24 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Interesting that you mention Honda, with this being a foreign make. By far the majority of generators on the U.K. market are sold with an unbonded neutral, as I believe are most in Europe. Perhaps this accounts for it?

Re: Transfer switch #74657
01/31/07 06:57 AM
01/31/07 06:57 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
That's odd, now that you mention it- I'd think it would be the other way around, as PME & shared earth/neutral is illegal in the US but more prevalent in Europe.

Boy that THAT throw me for a loop the first time I saw it! 3W WYE bus duct? Not very common in the US [Linked Image]

[This message has been edited by SteveFehr (edited 01-31-2007).]

Re: Transfer switch #74658
01/31/07 06:30 PM
01/31/07 06:30 PM
G
guschash  Offline OP
Member
Joined: Jan 2007
Posts: 12
Walbridge,Ohio,wood
This is a Honda, so if I don't tie neutrals together, how do the loads that will be running now on the generator get there neutal. From the generator?

Re: Transfer switch #74659
01/31/07 07:57 PM
01/31/07 07:57 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Guschash, here is a diagram from Ed MacLaren that shows a proper hook up for an unswitched neutral transfer switch.

Notice the generator neutral is not bonded to the generator housing.

[Linked Image]

Roger

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,245 Are you busy
189,203 Re: Forum
178,886 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.004s) Memory: 1.0245 MB (Peak: 1.1974 MB) Zlib enabled. Server Time: 2018-12-16 18:11:54 UTC