Sub-Panel
#73783
01/02/07 09:02 PM
|
Joined: Jun 2006
Posts: 7
OP
Junior Member
|
Is it legal to come off the bottom of an existing meter socket to a sub-panel other than the main breaker panel as long as wire is sized correctly and over-current protection is sized properly.
|
|
|
Re: Sub-Panel
#73784
01/02/07 09:17 PM
|
Joined: May 2002
Posts: 1,716
Member
|
The lugs in the Meter would have to be listed for mutiple conductors, the panel would have to be located in close proximity to the existing panel and have a main or no more than 6 breakers combined in the panels (with an exception for TVSS) see 230.70 thru 230.73.
It would not be treated as a "Sub-Panel" but as a Main panel
Roger
[This message has been edited by Roger (edited 01-02-2007).]
|
|
|
Re: Sub-Panel
#73785
01/02/07 09:19 PM
|
Joined: Dec 2004
Posts: 27
Member
|
Yes, you can if it is rated for a double tap.But it wouldn't be a sub panel, you would have another main breaker panel.
|
|
|
Re: Sub-Panel
#73786
01/02/07 09:22 PM
|
Joined: May 2002
Posts: 1,716
Member
|
Beameup, I think I was editing as you were posting.
Roger
|
|
|
Re: Sub-Panel
#73787
01/04/07 11:53 PM
|
Joined: Dec 2004
Posts: 27
Member
|
Yup, I think so. Oh well we both said the same thing ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
|
|
|
|
|