Posted By: ElJay Sub-Panel - 01/03/07 02:02 AM
Is it legal to come off the bottom of an existing meter socket to a sub-panel other than the main breaker panel as long as wire is sized correctly and over-current protection is sized properly.
Posted By: Roger Re: Sub-Panel - 01/03/07 02:17 AM
The lugs in the Meter would have to be listed for mutiple conductors, the panel would have to be located in close proximity to the existing panel and have a main or no more than 6 breakers combined in the panels (with an exception for TVSS) see 230.70 thru 230.73.

It would not be treated as a "Sub-Panel" but as a Main panel

Roger



[This message has been edited by Roger (edited 01-02-2007).]
Posted By: BEAMEUP Re: Sub-Panel - 01/03/07 02:19 AM
Yes, you can if it is rated for a double tap.But it wouldn't be a sub panel, you would have another main breaker panel.
Posted By: Roger Re: Sub-Panel - 01/03/07 02:22 AM
Beameup, I think I was editing as you were posting.

Roger
Posted By: BEAMEUP Re: Sub-Panel - 01/05/07 04:53 AM
Yup, I think so. Oh well we both said the same thing [Linked Image]