Washing machine #72864 12/11/06 07:31 PM
Joined: Mar 2002
Posts: 125
S
Sparks30 Offline OP
Member
Ran a new circuit 20 amp for washer,is there any code stating that it must be a dedicted circuit.Thanks Also how about the 220 and 120 volt wires being taped together for about half the run to a pvc pipe. Is this considered bundling.

[This message has been edited by Sparks30 (edited 12-11-2006).]

Work Gear for Electricians and the Trades
Re: Washing machine #72865 12/11/06 07:43 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
210.11(C)(2):

Quote
In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.

Re: Washing machine #72866 12/11/06 07:47 PM
Joined: Mar 2002
Posts: 125
S
Sparks30 Offline OP
Member
Thanks I missed that article. I did not do this work, another company did and the inspector pasted it. I am friends with the head inspector, just looking want somebacking when I talk to him about his help.

Re: Washing machine #72867 12/11/06 08:29 PM
Joined: Dec 2004
Posts: 209
H
HLCbuild Offline
Member
I read 210-11(C)2 as requiring a dedicated circuit for the laundry outlet(s) but 210-52(F) says you can have more than one outlet on this circuit. It just can't leave the laundry area.

Re: Washing machine #72868 12/11/06 09:08 PM
Joined: May 2006
Posts: 20
M
mister h Offline
Member
If you have a laundry sink within six feet of the edge the dedicated laundry circuit(210.11(C)(2) has to be GFCI protected. 210.8(7).

Ken


ken
Re: Washing machine #72869 12/11/06 09:34 PM
Joined: Apr 2003
Posts: 362
Obsaleet Offline
Member
gfci for the washer only if it is a duplex. It should be a single receptacle. Then it is a fixed appliance? And they won't have to call me to reset GFCI when it tripps [Linked Image]

Ob


Choose your customers, don't let them choose you.
Re: Washing machine #72870 12/11/06 09:41 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
There is no relief for a single appliance if the receptacle is within 6' of the sink.

Taped together for more than 2' is "bundled" but if you are using a 90c conductor you are still within the ampacity when you derate to 80%.


Greg Fretwell
Re: Washing machine #72871 12/11/06 10:24 PM
Joined: Mar 2002
Posts: 125
S
Sparks30 Offline OP
Member
There is no sink, just a washer and dryer. They want to use the duplex that is on the washer for a mini fridge and exhaust fan for the bathroom in the next room.

The wires that are taped together are #10-3 romex and #12-2 romex.

Re: Washing machine #72872 12/11/06 11:25 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
No dice on the exhaust fan and fridge in the next room. The circuit can't leave the laundry area or room for anything.


---Ed---

"But the guy at Home Depot said it would work."
Re: Washing machine #72873 12/12/06 06:36 AM
Joined: Mar 2002
Posts: 125
S
Sparks30 Offline OP
Member
The fridge is n the same room.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,741 Are you busy
209,655 Re: Forum
197,002 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3