Washing machine #72864
12/11/06 07:31 PM
12/11/06 07:31 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Ran a new circuit 20 amp for washer,is there any code stating that it must be a dedicted circuit.Thanks Also how about the 220 and 120 volt wires being taped together for about half the run to a pvc pipe. Is this considered bundling.

[This message has been edited by Sparks30 (edited 12-11-2006).]

Work Gear for Electricians and the Trades
Re: Washing machine #72865
12/11/06 07:43 PM
12/11/06 07:43 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
210.11(C)(2):

Quote
In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.

Re: Washing machine #72866
12/11/06 07:47 PM
12/11/06 07:47 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Thanks I missed that article. I did not do this work, another company did and the inspector pasted it. I am friends with the head inspector, just looking want somebacking when I talk to him about his help.

Re: Washing machine #72867
12/11/06 08:29 PM
12/11/06 08:29 PM
H
HLCbuild  Offline
Member
Joined: Dec 2004
Posts: 209
Herndon,Va USA
I read 210-11(C)2 as requiring a dedicated circuit for the laundry outlet(s) but 210-52(F) says you can have more than one outlet on this circuit. It just can't leave the laundry area.

Re: Washing machine #72868
12/11/06 09:08 PM
12/11/06 09:08 PM
M
mister h  Offline
Member
Joined: May 2006
Posts: 20
erie, pa. usa
If you have a laundry sink within six feet of the edge the dedicated laundry circuit(210.11(C)(2) has to be GFCI protected. 210.8(7).

Ken


ken
Re: Washing machine #72869
12/11/06 09:34 PM
12/11/06 09:34 PM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
gfci for the washer only if it is a duplex. It should be a single receptacle. Then it is a fixed appliance? And they won't have to call me to reset GFCI when it tripps [Linked Image]

Ob


Choose your customers, don't let them choose you.
Re: Washing machine #72870
12/11/06 09:41 PM
12/11/06 09:41 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
There is no relief for a single appliance if the receptacle is within 6' of the sink.

Taped together for more than 2' is "bundled" but if you are using a 90c conductor you are still within the ampacity when you derate to 80%.


Greg Fretwell
Re: Washing machine #72871
12/11/06 10:24 PM
12/11/06 10:24 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
There is no sink, just a washer and dryer. They want to use the duplex that is on the washer for a mini fridge and exhaust fan for the bathroom in the next room.

The wires that are taped together are #10-3 romex and #12-2 romex.

Re: Washing machine #72872
12/11/06 11:25 PM
12/11/06 11:25 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
No dice on the exhaust fan and fridge in the next room. The circuit can't leave the laundry area or room for anything.


---Ed---

"But the guy at Home Depot said it would work."
Re: Washing machine #72873
12/12/06 06:36 AM
12/12/06 06:36 AM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
The fridge is n the same room.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,231
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,011 Are you busy
181,006 Re: Forum
171,251 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.005s) Memory: 1.0220 MB (Peak: 1.1974 MB) Zlib enabled. Server Time: 2018-02-18 21:53:30 UTC