#72577 - 12/04/06 05:45 PM Should a metal chain-link fence be grounded?  
Rich Thomas  Offline
Member
Joined: Mar 2005
Posts: 48
Seattle, Washington, USA
This is for the design of a new 100KW, 277-480V engine-generator installation. The E/G will be mounted on a reinforced concrete pad. The pad will contain rebar grounding, and a buried ground ring with a ground rod at each corner. A chain-link fence will encircle the pad. There is nothing electrical mounted on, or near the fence. As far as I can see, the fence cannot become energized from the E/G equipment.

Do you recommend connecting the fence to the grounding electrode system for the generator/pad?

If yes, what is your recommended procedure? Should each post have a bolted connection to the grounding system?

Thanks for your input.


Work Gear for Electricians and the Trades

#72578 - 12/04/06 07:34 PM Re: Should a metal chain-link fence be grounded?  
livetoride  Offline
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
You did not state enough info but the fence most likely should be BONDED. My thought. Rod


#72579 - 12/04/06 07:50 PM Re: Should a metal chain-link fence be grounded?  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
On the job you described, we have a professional engineer, supply the plans with a detail of all the bonding, this is a design issue.


#72580 - 12/04/06 08:25 PM Re: Should a metal chain-link fence be grounded?  
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 791
Chicago, Il.
I know that if I was the guy inside the fence, working on the genny, and could touch both, I would feel better knowing they're bonded.
Joe


#72581 - 12/04/06 11:18 PM Re: Should a metal chain-link fence be grounded?  
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
If it was a HV substation, it would be bonded, just so everything's at equipotential.

I doubt the fenc e is "likely to be energized" unless you have OH wiring or other hazards. But nothing is impossible. You have to decide if it's improbable.

If I was doing it, I'd ground it!



Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7686 MB (Peak: 0.9055 MB) Zlib enabled. Server Time: 2017-12-11 03:53:13 UTC