This is for the design of a new 100KW, 277-480V engine-generator installation. The E/G will be mounted on a reinforced concrete pad. The pad will contain rebar grounding, and a buried ground ring with a ground rod at each corner. A chain-link fence will encircle the pad. There is nothing electrical mounted on, or near the fence. As far as I can see, the fence cannot become energized from the E/G equipment.

Do you recommend connecting the fence to the grounding electrode system for the generator/pad?

If yes, what is your recommended procedure? Should each post have a bolted connection to the grounding system?

Thanks for your input.

Joined: Jan 2005
Posts: 109
L
Member
You did not state enough info but the fence most likely should be BONDED. My thought. Rod

Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
On the job you described, we have a professional engineer, supply the plans with a detail of all the bonding, this is a design issue.

Joined: Nov 2005
Posts: 827
J
Member
I know that if I was the guy inside the fence, working on the genny, and could touch both, I would feel better knowing they're bonded.
Joe

Joined: Oct 2004
Posts: 132
M
Member
If it was a HV substation, it would be bonded, just so everything's at equipotential.

I doubt the fenc e is "likely to be energized" unless you have OH wiring or other hazards. But nothing is impossible. You have to decide if it's improbable.

If I was doing it, I'd ground it!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
Trumpy 7
NORCAL 5
Popular Topics(Views)
300,340 Are you busy
230,001 Re: Forum
214,810 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5