I am installing a 35 kw generator to backup a 70 amp 3 phase sub panel. My question is if the building has a delta high leg service, will this effect the generator?

Horizontal Ad
#69961 09/26/06 01:34 PM
Joined: Jul 2004
Posts: 787
L
Member
ASSume voltage is 120/240 center tapped delta.

What are the loads on the sub panel? All single phase, all 3 phase, or mixed? If mixed, can the generator supply them, or are you going to use a transformer? Remember the issues with SDS and grounding through transfer switches.

#69962 09/26/06 02:27 PM
Joined: Feb 2005
Posts: 13
J
jersey Offline OP
Member
With the 3-3 phase refridgerator units and single phase 240v water pump each leg was drawing around 31 amps apiece. Thera are other small loads.

#69963 09/26/06 02:34 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Can you get a generator that will supply 120/240 3 phase 4 wire?
Don


Don(resqcapt19)
#69964 09/29/06 09:06 AM
Joined: Feb 2005
Posts: 13
J
jersey Offline OP
Member
the guardian type. They make 3 phase generators

#69965 09/29/06 09:33 AM
Joined: Nov 2000
Posts: 2,148
R
Member
jersy,
Quote
the guardian type. They make 3 phase generators
They are all 3 phase wye connected units. That is not the same as a 3 phase delta system with a high leg. I have never seen a generator that could be connected 3 phase delta with a high leg. I have only seen that configeration on transformers.
Don


Don(resqcapt19)
#69966 09/29/06 12:40 PM
Joined: Jul 2004
Posts: 787
L
Member
When I repaired generators many years ago, the small gennys on reefer trucks were 3 phase 240 delta. I don't know if they where available in anything larger than 5 or 10 KW.

If the Guardian you are talking about has a 12 lead alternator, you could rewire it for 120/240 delta with a high leg. I would check with the factory about the maximum unbalanced load.

Larry

Horizontal Ad
#69967 09/30/06 09:11 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Larry,
Quote
If the Guardian you are talking about has a 12 lead alternator, you could rewire it for 120/240 delta with a high leg.
I didn't look at all of the wiring diagrams, but on the ones that I did look at, the center of the wye was an internal connection.
Don


Don(resqcapt19)
#69968 10/05/06 09:52 AM
Joined: Feb 2005
Posts: 13
J
jersey Offline OP
Member
Just talked to guardian . There 3 phase units not compatible with a delta system. I have a meat packing plant that needs emergency back-up . Power always goes out they dont want there meat to go bad. Is ther an other way to go?

#69969 10/05/06 10:04 AM
Joined: Feb 2005
Posts: 13
J
jersey Offline OP
Member
one more question , Why would it matter if the back-up generator Was a wye ? The equipment would work 3 phase, delta or wye connected

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Top Posters(30 Days)
davey 1
dsk 1
Popular Topics(Views)
554,541 Are you busy
428,778 Re: Forum
398,709 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5