#69960 09/26/06 02:12 PM
jersey Offline OP
I am installing a 35 kw generator to backup a 70 amp 3 phase sub panel. My question is if the building has a delta high leg service, will this effect the generator?
#69961 09/26/06 02:34 PM
ASSume voltage is 120/240 center tapped delta.
What are the loads on the sub panel? All single phase, all 3 phase, or mixed? If mixed, can the generator supply them, or are you going to use a transformer? Remember the issues with SDS and grounding through transfer switches.
#69962 09/26/06 03:27 PM
jersey Offline OP
With the 3-3 phase refridgerator units and single phase 240v water pump each leg was drawing around 31 amps apiece. Thera are other small loads.
#69963 09/26/06 03:34 PM
Can you get a generator that will supply 120/240 3 phase 4 wire?
Don
#69964 09/29/06 10:06 AM
jersey Offline OP
the guardian type. They make 3 phase generators
#69965 09/29/06 10:33 AM
jersy,
They are all 3 phase wye connected units. That is not the same as a 3 phase delta system with a high leg. I have never seen a generator that could be connected 3 phase delta with a high leg. I have only seen that configeration on transformers.
Don
#69966 09/29/06 01:40 PM
When I repaired generators many years ago, the small gennys on reefer trucks were 3 phase 240 delta. I don't know if they where available in anything larger than 5 or 10 KW.
If the Guardian you are talking about has a 12 lead alternator, you could rewire it for 120/240 delta with a high leg. I would check with the factory about the maximum unbalanced load.
Larry
#69967 09/30/06 10:11 AM
Larry,
I didn't look at all of the wiring diagrams, but on the ones that I did look at, the center of the wye was an internal connection.
Don
#69968 10/05/06 10:52 AM
jersey Offline OP
Just talked to guardian . There 3 phase units not compatible with a delta system. I have a meat packing plant that needs emergency back-up . Power always goes out they dont want there meat to go bad. Is ther an other way to go?
#69969 10/05/06 11:04 AM
jersey Offline OP
one more question , Why would it matter if the back-up generator Was a wye ? The equipment would work 3 phase, delta or wye connected
