#68234 07/30/06 12:08 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Bidding tight on multi town home project, sometimes best practice takes a back seat,and I have a question on code for these; can exterior recs. come from nearest circuit or must they be dedicated 20a circuits? Thanks.

Horizontal Ad
#68235 07/30/06 12:24 PM
Joined: Jul 2004
Posts: 10,026
Likes: 37
G
Member
The code is silent on where the outside general purpose outlets are served from. Just don't hang them on the inside circuits that can't have "other outlets" like the laundry, kitchen and bath.


Greg Fretwell
#68236 07/30/06 12:53 PM
Joined: Jun 2005
Posts: 821
S
Member
I feed outside receptacles that are required by article 210.52 (E) from the nearest lighting circuit. The front receptacle is rarely on the same circuit as the one in the rear to save on wire expenses. I see nothing in the mentioned article about needing an individual 20amp branch circuit.

Good luck!


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
553,511 Are you busy
428,122 Re: Forum
398,270 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5