ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 4
Recent Posts
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
Bathroom electrical
by gfretwell. 08/14/17 02:05 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,870 Are you busy
175,422 Re: Forum
167,719 Need opinion
Who's Online Now
0 registered members (), 27 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#66181 - 05/23/06 07:39 PM Pump Motor Overamping  
drillman  Offline
Member
Joined: Mar 2003
Posts: 97
Somewhere in Texas
Got a motor driven pump. 75 HP, 3 phase, 460 V, SF 1.15. Nameplate FLA is 87A. The pump is on a constant flow system.

Amprobed it at 96, 100, 104 amps. Voltages are within 2 volts of each other.

Is this something I should be worried about? 87 X 1.15 is 100. I am not concered with the imbalance as much as the fact that the motor is running at max all the time.

I know next to nothing about pumps so is this something I should worry about? This motor/pump combo is a backup to another pump that just failed. It has not run in about 2 years .

Many thanks


Work Gear for Electricians and the Trades

#66182 - 05/24/06 02:40 AM Re: Pump Motor Overamping  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
drillman -

You most likely want to be concerned about the imbalance, as it amounts to 4%.

The winding temps of the motor will encrease, efficiency will decrease, and life expectancy of the motor windings will decrease drastically.

Go to This Link

for a good article explaining the adverse effects of unbalanced voltage.

Steve


(edited to add link)



[This message has been edited by electure (edited 05-24-2006).]


Thanks
Steve

#66183 - 05/24/06 02:00 PM Re: Pump Motor Overamping  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
drillman -

I read your post last night and "saw" "amps" and then "thought" "voltage".

The info in my previous post does not apply, but I'll leave it in case anyone would like to get info about "voltage imbalance".

I'll email you an article about current imbalance, as I don't think it would cut-n-paste well.

While you have a 4% unbalance, it looks as if you are ok.

It is not unusual to have higher unbalance at no load than when the motor is under load. Were you reading taken under load or no load?

Steve


Thanks
Steve

#66184 - 05/24/06 04:00 PM Re: Pump Motor Overamping  
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
What is the voltage at the motor?


#66185 - 05/24/06 11:22 PM Re: Pump Motor Overamping  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
The fact that this is a backup to a pump that just failed is cause for concern. It could be the pump/motor combination is undersized for the application. Has something been changed since the initial installation? If it is a centrifugal pump, you can throttle the discharge valve a notch or two to drop the current, maybe you will still have acceptable flow with the throttled valve. Either way you should take a second look at the system, compare field conditions with design values. Good luck.



Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7684 MB (Peak: 0.9063 MB) Zlib enabled. Server Time: 2017-08-17 09:45:56 UTC