Where in the code does it say you can only load a breaker to 80%?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#65631 05/09/06 03:23 PM
Joined: Aug 2003
Posts: 64
E
Member
I think you are thinking of 210.20(A). The rule only applies for continuous loads. Note that requiring the OCPD to be not less than 125% of the continuous load is another way of saying that the continuous load may not be more than 80% of the OCPD rating.