Derating #65630
05/09/06 01:56 PM
05/09/06 01:56 PM
R
rocha12  Offline OP
Junior Member
Joined: May 2006
Posts: 5
Where in the code does it say you can only load a breaker to 80%?

Work Gear for Electricians and the Trades
Re: Derating #65631
05/09/06 03:23 PM
05/09/06 03:23 PM
E
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
I think you are thinking of 210.20(A). The rule only applies for continuous loads. Note that requiring the OCPD to be not less than 125% of the continuous load is another way of saying that the continuous load may not be more than 80% of the OCPD rating.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,506 Are you busy
186,194 Re: Forum
175,656 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9411 MB (Peak: 1.0591 MB) Zlib enabled. Server Time: 2018-08-14 08:27:10 UTC