#65630 - 05/09/06 01:56 PM Derating  
rocha12  Offline
Junior Member
Joined: May 2006
Posts: 5
Where in the code does it say you can only load a breaker to 80%?


Work Gear for Electricians and the Trades

#65631 - 05/09/06 03:23 PM Re: Derating  
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
I think you are thinking of 210.20(A). The rule only applies for continuous loads. Note that requiring the OCPD to be not less than 125% of the continuous load is another way of saying that the continuous load may not be more than 80% of the OCPD rating.



Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.004s) Memory: 0.7426 MB (Peak: 0.8584 MB) Zlib enabled. Server Time: 2017-10-18 20:19:19 UTC