347 lighting #62337
02/15/06 02:21 AM
02/15/06 02:21 AM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Is it proper lockout procedure to shut off the other 2 phases sharing the neutral with thge circuit you are working on?

Work Gear for Electricians and the Trades
Re: 347 lighting #62338
02/15/06 08:26 AM
02/15/06 08:26 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
yes


Don(resqcapt19)
Re: 347 lighting #62339
02/15/06 09:03 AM
02/15/06 09:03 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
With power left on two other phases sharing the neutral, if you lifted that neutral at some point you could end up with voltage on one side via the loads.

Not only would this represent a shock-risk to you, it could also unbalance the voltages on those other loads. Given a large load on one phase and a small load on the other, you could see the voltage across the latter rise to almost the phase-to-phase level.

Re: 347 lighting #62340
02/15/06 10:16 PM
02/15/06 10:16 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You know, this is one thing NEVER mentioned in "lock-out' discussions. The same point also applies to single phase, multi-wire circuits- that is, where two 'legs' share a neutral!

I found this out the hard way...when a money changer was momentarily supplied with 220v...I really loved having to buy a $600 power supply (as part of a $100 add-a-receptacle job)!

An added clarification....if you are "downstream" of any point where the other circuits might be, then there is no need to isolate them as well. But if...as is often the cas...you have all phases present in the run of lights, they all ought to be killed.

[This message has been edited by renosteinke (edited 02-15-2006).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,621 Are you busy
186,362 Re: Forum
175,824 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9589 MB (Peak: 1.0908 MB) Zlib enabled. Server Time: 2018-08-19 07:35:13 UTC