ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 449 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#6202 12/26/01 03:22 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
Is this something that can be described in 24 words or less?
Don't want to burden anyone with having to write a book like the last question I asked, much appreciated though.
C

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#6203 12/26/01 04:50 PM
Joined: Oct 2000
Posts: 5,393
S
Member
My 2 ct's;

Capactive Coupling is the reactance of EMF to proximal items.

PS......
( while back when i thought i was a nuetral, Scott explained that i was indeed more of a capactitor..)

#6204 12/26/01 06:42 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
2 conductors separated by an insulator make a capacitor. Capacitors will pass AC. Therefore, one live wire can cause a voltage in a de-energized conductor.

23 words, one number & one acronym. Close enough?

Tom

[This message has been edited by Tom (edited 12-26-2001).]


Few things are harder to put up with than the annoyance of a good example.
#6205 12/26/01 07:03 PM
Joined: Aug 2001
Posts: 7,520
P
Member
I'm sure the folks here don't mind giving longer explanations, just so long as you don't mind reading them. [Linked Image]

The actual capacitance between two conductors (measured in farads, or more commonly a smaller division such as the microfarad) will depend upon:

(a) the area of those conductors,
(b) the distance between them, &
(c) the type of insulation material between them (known as a dielectric).

Once you have calculated or measured capacitance value, you can determine the reactance (& thus the current that will flow) from:

X = 1 / (2 x pi x f x C)

where f=frequency in use & C=capacitance in farads). X will be in ohms.

#6206 12/26/01 07:06 PM
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
A really quick and dirty description would be:

All circuits exibit various levels of Capacitance, which is external from the circuit conductors. In order for larger currents to flow, the external Capacitive Fields must be charged to a [somewhat] constant level.
This "Line Charging" is between any and all points of different Potential.

Line charging "Couples" insulated and isolated circuit conductors to each other, via the Capacitive Effects between conductors and points of different Potentials.

Simply, between any and all circuit conductors, there's a Capacitive Charge that must be created and held during current transfers, or prior to current transfers - like a circuit opened with a toggle switch, or a closed circuit with no connected loads [Receptacle branch circuits, for example].

For conductors inside of a conduit, the Capacitive circuits are between all conductors, and all conductors and the conduit. Also there's a Capacitive Charge between the conduit and the Earth ground.

For Utility power systems, there's a Capacitive Charge between the circuit conductors, and between each conductor and the Earth Ground.

Between Utility sides and "User Sides" [Primary / Secondary], the Capacitive Coupling occurs primarily across the Transformer's windings, but also occurs between the Coupled effects on the Primary to Earth Ground, and the Secondary to Earth Ground circuits.

These are when Ungrounded AC systems' voltage to ground become really excessive.

Roughly, the Capacitive Coupling effect is present whenever there's current flowing, or available to flow on circuits, and there's any difference in Potential - either externally or internally to the conductors.

Kind of trick stuff, isn't it???

A working example to use is:
Line Charging [Capacitive Coupling] is the reason GFCIs aren't set to trip when the slightest inbalance of current is sensed.
If the GFCI was set to trip at as low as 1 milliamp, circuits with lengths of like 100 feet [for example] would trip the GFCI, and the circuit being protected would be in proper working condition [AKA no one is being shocked].

Sorry to be so technical in the explanations.

It's just great that you are here asking these questions!!! It would be nice if I can figure an easy way to explain this stuff, so it's not quite as overwhelming.

Good luck with your studies!

Scott S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#6207 12/26/01 07:59 PM
Joined: May 2001
Posts: 717
G
Member
Geeez Scott, great answer (Great Scott, geeez what an answer, with deference to Jimmy Olson/Perry White for us geezers).

Cindy it means you can have a voltage present in an uncharged conductor because of it's near proximity to an charged conductor. For all practical purposes, there's nearly no difference between capacitive and inductive coupling. Also because of another thread I've been in lately, it does not happen in DC conductors, only ones with a frequency.

There have been real problems with control circuitry run with load conductors in conduits because when you push the stop button, it won't because of coupling. that's the normal danger. It also becomes apparent when you run low voltage conductors in the same manhole, etc., with medium (high)voltage conductors, it has killed more than one.

OK, coulda been "Great Caesars Ghost" on the TV show. [Linked Image]

#6208 12/26/01 08:14 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
Great answer Scott. I would also like to jump in with Mr. Corron and add that it is very important in medium and high voltage applications that the discharge the conductors when working on equipment. The conductors will hold a charge.


The Watt Doctor
Altura Cogen
Channelview, TX
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#6209 12/26/01 09:49 PM
Joined: Oct 2000
Posts: 4,161
Likes: 5
Member
George,

"Great Caesars Ghost" sounds like the right one. They even had an episode where someone dressed up like Caesar to come to Perry in a dream for some reason.

Bill


Bill
#6210 12/26/01 11:13 PM
Joined: May 2001
Posts: 717
G
Member
Not that I remember of course, not having been born yet.....ahem. They were trying to make Perry think he was crazy, his statue of Caesar also talked.
Sorry to change subjects on ya, Cindy, but you know were subject to 'wing' off into a tangent at any moment.

#6211 12/26/01 11:55 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
before i go too far here, when you use a megger to test a large service [~1200A]that has recently been deenergized, you use an aligator clip and probe tool, or something similar, to discharge the bus bar so you dont get zapped. the charge that builds up on the bus, is it correct to say that was from a capacitive coupling with the other conductors?

from pauls reactance formula, i can see how higher frequency and capacitance numbers will make lower capacitive reactance values. since its in ohms like resistance, then lower capacitive reactance is better, right? but it takes higher capacitance to get the lower reactance, or resistance if i can say that, which is a good thing. so higher capacitance is not all bad?

capacitive coupling across primary and secondary? how much of an affect does this have in farads or ohms for normal installations sized per code, any percentages? also how much coupling is normal between primary and secondary grounds?

my brain hurts, gotta stop for now -C-

#6212 12/27/01 01:13 AM
Joined: Dec 2001
Posts: 300
M
Member
Capacitive Coupling in 14 words:

Current in wire 1 causes magnetic field. Magnetic field causes current in wire 2.

Actually the wires can also "transfer" current because of the charge on one wire affecting the charge on the other (the like charges repel and opposite charges attract thing). It's probably both the magnet field thing and electrical charge thing that makes it happen but you asked for brevity.

And the charge that "accumulates" on the bus bar isn't capacitive "coupling" although it does happen because the system acts like a big capacitor. The grounded set of wires acts like one capacitor plate and the hot wires running along side those act like the other capacitor plate.

I like your questions. What's your story? What do you do? Why all the questions?

[This message has been edited by maintenanceguy (edited 12-27-2001).]

#6213 12/27/01 10:23 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
Current in wire 1 causes magnetic field. Magnetic field causes current in wire 2.
I thought that was induction.
Don(resqcapt19)


Don(resqcapt19)
#6214 12/27/01 11:20 AM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
i've been an electrician for several years now but realize i'll always be learning or relearning, just when you think you know something, poof, gone or relearned differently.

anyway what are we calling the force that "transforms" energy from the primary to the secondary? isnt it induction?

#6215 12/27/01 11:34 AM
Joined: May 2001
Posts: 717
G
Member
See what I mean ? There is very little PRACTICAL difference between capacitive and inductive coupling ! Hard to tell the difference for the field electrician, and they both produce nearly the same results, unless we get into an RF discussion, and that means communications (usually wireless) and scif rated computer rooms.

#6216 12/27/01 02:34 PM
Joined: Aug 2001
Posts: 7,520
P
Member
When current flowing in wire #1 creates a magnetic field which then generates a current in wire #2, that's inductive coupling. It's the principle utilized by every transformer.

Capacitive coupling is concerned with electric fields rather than magnetic ones. In practice, when wires are close enough to provide inductive coupling they're also going to be close enough for some capacitive coupling, so there will always be some capacitance between the primary and secondary windings of a transformer, for example.

Perhaps a couple of worked examples might help. Let's say you have a length of feeder with a measured capacitance between hot & neutral of 0.5uF (microfarads). Such a value is not hard to achieve with a moderately long cable.

Assuming a U.S. supply of 120V at 60Hz, the reactance will be

X = 1 / (2 x 3.142 x 60 x 0.0000005)
= 5300 ohms approx.

That reactance is directly across the supply, so (ignoring the series resistance of the wiring, which is negligible by comparison) there will be a capacitive current of

I = 120V / 5300 ohms = 0.0226 A

True enough, 22mA is hardly going to be a problem compared to the probable load on that feeder, and because it is reactive current it isn't actually consuming any power anyway.

BUT -- Consider that you could just as easily have 0.5uF between hot & ground.
See why trying to feed this with a sensitive GFI would give you a problem?

Now an example of series reactance. Assume power is going to a light fixture with a 2-wire loop from there to the switch. With the switch off and bulb removed, the hot wire from switch to light is effectively diconnected from the system. If you took a voltmeter and measured from that wire to ground (or neutral), you would expect a zero reading, right? This is where using a modern high-impedance digital meter can cause confusion.

Let's say the capacitance between the two wires of the switch loop is 0.001uF - Again, not too difficult to achieve.

The capacitive reactance is

X = 1 / (2 x 3.142 x 60 x 0.000000001)
= 2.66 megohms

Hey, that's pretty high isn't it? Surely that won't have much effect on anything?

Well, the input of a typical DMM is 10 megohms. So in effect we have 2.66 meg of capacitive reactance in series with a 10 meg resistance (the meter will actually have a small amount of capacitance of its own across that 10M,
but it's small so we'll ignore it for our present purpose - I'm trying to keep it as simple as possible).

OK, now although reactance and resistance are both measured in ohms, we can't just add them together because the voltages across them are not in phase. So we have to use Pythagoras, with impedance (Z) as the hypotenuse of a right-triangle:

Z = SQRT ( R^2 + X^2 )

So

Z = SQRT ( 10^2 + 2.66^2 ) = 10.35 Meg

Stick wih me, it gets eesier now [Linked Image]
Here's the simple bit:

I = 120V / 10.35 megohms = 11.59 uA.

Only 11.59 microamps going through the meter. Now work out the voltage across the meter:

V = 11.59uA x 10 megohms = 115.9 volts.

Say what??!! Nearly 116V to ground on a conductor that isn't connected to a power source? Yep, that's right, and it's all because of the capacitive coupling.

In practice, the capacitance of the meter would pull that figure down a little, and there would be other things to consider; e.g. If that switch cable had a ground wire then the capacitance between the open conductor & ground would have a considerable effect. But you get the idea.

As you observed, Cindy, at higher frequencies the reactance is lower for any given value of capacitance. When we get to talking about UHF TV or SHF satellite frequencies, moving a wire by a quarter-inch can somtimes mean the difference between perfect and nothing.

OK, you can all wake up at the back there now... [Linked Image]

#6217 12/27/01 06:40 PM
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Paul,

Excellent post!!! Very well structured.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#6218 12/27/01 06:59 PM
Joined: Aug 2001
Posts: 7,520
P
Member
Thank you (Blush!)

I'm just visiting old ground here. I did a couple of articles on inductive and capacitive reactance, resonance, etc. for Popular Electronics a few years ago.

Cindy,
I nearly forgot this: You were working on an assumption that a lower capacitive reactance might always be better.

In the words of an old song, "It ain't necessarily so."

In the case of leakage current from hot ground in a long feeder causing GFI trips, you would want to aim for a lower capacitance (i.e. a higher reactance) to reduce that unwanted current.

That's not to say that the higher capacitance might not have some beneficial effects, such as helping to filter out harmonics.

In some cases you're not aiming for reactance as high or as low as possible, but for a certain optimum value. The capacitor in a split-phase motor is a good example.


[This message has been edited by pauluk (edited 12-27-2001).]

#6219 12/28/01 01:10 AM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
seriously dont worry about answering this if its too much, i copied all of this to a word document and tried to sort out mostly scotts and pauls replies, but if you dont answer anything else, please tell me how the electricians in the UK refer to 1/2" EMT or 3/4" flex, for instance if i asked them for
a stick of 1/2" EMT would they say: 'eres yer 13-millimeter EMT matey [Linked Image] also think i've heard 1/2" rigid referred to as 16 metric maybe, not 13?

You said this: Capacitive Coupling effect is present whenever there's current flowing, or available to flow on circuits, and there's any difference in Potential - either externally or internally to the conductors.

Questions: Do you have examples of the difference in potential "externally"? Vs "internally"?

You said this: Let's say you have a length of feeder with a measured capacitance between hot & neutral of 0.5uF (microfarads). Assuming a U.S. supply of 120V at 60Hz, the reactance will be: X = 1 / (2 x 3.142 x 60 x 0.0000005) = 5300 ohms approx. That reactance is directly across the supply, so (ignoring the series resistance of the wiring, which is negligible by comparison) there will be a capacitive current of: I=120V / 5300 ohms = 0.0226 A.

Questions: What do you mean “that reactance is directly across the supply”? Potential difference? Electric field? Does the “line charging” ‘couple’ hot to hot, hot to neutral, hot to ground, and neutral to ground? Does capacitive coupling result in reactance and current flow only between those conductors coupled to each other? In other words, lines A and B are coupled, but lines B and C are not close enough to couple, so how does the capacitive coupling current flow in line A or line B relate to line C? If line B touches line C does it discharge? It seems like we’re talking about 2 effects, capacitive coupling results in current flow, and capacitive coupling results in reactance that inhibits current flow.

You said this: 22mA is hardly going to be a problem compared to the probable load on that feeder, and because it is reactive current it isn't actually consuming any power anyway.
Also you said: Although reactance and resistance are both measured in ohms, we can't just add them together because the voltages across them are not in phase.

Questions: What is the difference? Is reactive current like a different sine wave, different phase, or beyond my comprehension at this point?

Questions: In the example there is 2.66 megohms capacitive reactance in the light switch legs tested with a digital meter. Why is there 10 megohms of resistance in the meter? Why can you use 120v in the I=ExR formula since we started with an open circuit without voltage on it?

You said this: In some cases you're not aiming for reactance as high or as low as possible, but for a certain optimum value. The capacitor in a split-phase motor is a good example.

Question: Is there a short explanation for this, or is that another thread?
thanks -C-

#6220 12/28/01 07:32 PM
Joined: Aug 2001
Posts: 7,520
P
Member
Wow, that's some batch of questions!

Q. Reactance across supply, etc.

In the case of the long feeder, it just means that the 0.5uF capacitance is in parallel with the supply.

Have you studied the construction of a basic capacitor? You can make a very crude one by taking a couple of strips of aluminum kitchen foil, sandwiching a slightly wider strip of thin insulating material between them and on top, then rolling the whole lot into a cylinder with one wire connected to each foil. In earlier times capacitors were often just that, with waxed paper as the insulation.

The point is that it is nothing more than two strips of metal held a short distance apart by an insulating dielectric. If you took a 0.5uF capacitor and connected it between a hot breaker terminal and neutral busbar at a panel, you would get 22mA of current flowing through that capacitor.

A cable is also two long strips of metal with insulating material between them, so if you make it long enough you can get the same 0.5uF (or more). The capacitor just packs it into a much smaller space by deliberately minimizing the gap between the conductors and getting the most surface area in the smallest possible space.

So, the 0.5uF capacitor above has one foil connected to the hot and the other to the neutral. The two wires in the long feeder cable are also connected one to hot, one to neutral, so it's a parallel capacitance.

You'll get such a capacitance between any two such conductors which are close enough. If you took a length of, say, 3-wire armored cable, there would be a measurable capacitance line A to line B, B to C, and A to C. There would also be capacitance between each of those lines and the grounded armor.

The longer the cable, the higher the capacitance will be. The greater the spacing between conductors, the lower the capacitance.

Regarding your two effects: In the very broadest of terms, just placing capacitance in parallel with the supply will cause additional current to flow, while adding capacitance in series with some other device will increase the overall impedance and reduce the current flow, so you're on the right track.

HOWEVER, this is not necessarily the case where the rest of the circuit contains inductance (e.g. a motor, fluorescent lamp ballast etc.). The explanation for that had better wait until later.

Q. Difference between reactive/resistive ohms, why we can't add them directly.

Basically because there is a phase difference between the resistive and the capacitive portion of the circuit. In this case of the meter, it is a series circuit. The voltage across the resistive section (the meter) will be in phase with the current, but the voltage across the capacitive section will lag the current by 90 degrees.

Q. Why 10 meg input on a DMM.

That's the way the circuitry is designed. High-impedance meters are needed for some sensitive electronics to avoid loading effects, and that's the field in which the DMM first appeared. 10M has just become a common design value, although there are others.

Q. Why did we use 120V on the I=E/R (or more precisely, I=E/Z).

At first look you might think that the meter started on an open circuit, but we've already seen that that "open" conductor was really capacitively coupled to the energized hot wire.

The impedance (Z) calculated was that of the meter resistance (R) and the cable reactance (X) in series, so we need to use the voltage appearing across the whole series circuit. That's from the energized hot wire to neutral, i.e. 120V.

Q. Optimum value of reactance.

I'd better not get into too long an explanation, but the power-factor correction capacitor would be a good example.

Inductance (e.g. a fluoro. ballast) causes a phase shift between current and voltage on the supply which is undesirable (i.e. the power factor is less than 1).

Fitting a p.f. capacitor of the correct value can bring I and E back in phase (or very nearly so). Too small and the phase shift will not be enough to do that; too big and you'll "overshoot" and take it out of phase again in the other direction.

Notes on conduit later... Must eat! [Linked Image]

#6221 12/28/01 09:20 PM
Joined: Aug 2001
Posts: 7,520
P
Member
Cindy,

If you went into a store here and asked for any size EMT, you'd be more likely to get a reply like "EMT guv? What's that then?" [Linked Image]

Just another of those American things which hardly anybody here knows about, along with Edsels and Gilligan's Island!

We don't have an EMT equivalent. There was some thinwall conduit used way back pre-war, but it hasn't been made for decades.

Heavy-gauge steel conduit is available in galvanized and black enamel finishes. The smallest sizes are 20 and 25mm, which replaced the old 3/4 and 1" types.

I've never heard of a 16mm gauge, though it might exist in some other country.

We do have 15 mm copper water pipe though. It replaced the 1/2-inch type in the 1970s, but is almost exactly the same size, because the 1/2-inch was measured as the bore and the 15mm is outside diameter.

#6222 12/29/01 06:34 AM
Joined: Oct 2000
Posts: 5,393
S
Member
a good thread here. [Linked Image]
It sheds light on Soares using the term 'Capacitive Coupling' as pertains to a delta system.

#6223 12/29/01 01:36 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
thanks so much to everybody that added their thots, this was totally helpful. raised more questions but is a good catalyst for getting back to my old books. you probably think i havent studied any of this before but, embarrassed to say that i have, and forgot a lot of it or maybe thot i knew it but apparently misunderstood, but was able to get enuf right on tests to get thru [Linked Image] in the field you're busy working and figuring out ways to save time & cut corners & stay up with the [pardon me frinch] freeking codes, not much time to think [Linked Image]

not rocket science, but anyway these concepts were very helpful to get straight: the inductive "magnetic field" coupling between transformer primaries to secondaries vs. the "electric field" capacitive coupling
[line charging] of something like long GFCI circuits that could make enuf current to trip them if their settings were too low.
and this from another thread, seeing that the electrons are trying to return to their source instead of the earth [really just another big conductor]. i think when i re-read my books these ideas will put it a new perspective.

kind of a last thing that might help is examples if anyone has any that might bring this back down to a "working in the field" level, like scotts Line Charging [Capacitive Coupling] GFCI example, or george's motor not stopping, [sorry but the Caesars Ghost thing must have been from years B.C.indy, didnt help], & paul's switch loop.

when you wire a fluorescent ballast, its just wiring to the ballast, where is the power factor correction capacitor that adjusts for the phase difference in the current and voltage?

there's a capacitor in a control box mounted in a pump house for submersible pumps, what is that doing? starting circuit vs. running circuit, right? sorry, thot i was thru asking questions [Linked Image]

any other capacitors i should be familiar with that i probably work with regularly? and why they're used?
-C-

#6224 12/29/01 03:24 PM
Joined: Aug 2001
Posts: 7,520
P
Member
I guess for many people who want to know just enough to do their job, the theoretical side can seem daunting and even unimportant. But I'm firmly of the opinion that we should understand WHY we do something (instead of just saying "because that's the way it's done"). That theory may suddenly become very useful when running up against a less common problem.

Of course, I'm just an electronics nut who's wanted explanations of everything since the age of about 5. Others may see it differently!

The capacitor in the control gear of the pump motor is most likely part of the normal split-phase induction motor. It's used to generate the appropriate phase shift to the auxiliary windings to obtain the rotating field needed to start the rotor turning.

There are some variations in fluoro. light wiring. I don't think I ever had cause to open one up while I was in America, so the others will have to clarify that point.

Most conventional fluoro's in the U.K. have the p.f. correction capacitor just clipped inside the housing and wired directly across hot & neutral at the terminal block. Many cheaper types sold for domestic use don't bother with it; the lower p.f. of one or two fittings is considered inconsequential. (And it saves all of $2 per fitting!)

Capacitors are used widely throughout electronics, but one other area that may be of concern to you is filters in power supplies.

These typically have caps. connected H-N, N-G, and H-G in combination with some series inductors. It's becoming more of a problem in big offices, etc., where with dozens of computers in use the leakage current to ground can be appreciable.

#6225 12/29/01 04:10 PM
Joined: May 2001
Posts: 717
G
Member
I like teaching, but the 2nd semester of the year is also open to all electricians, apprentices and journeyman alike. I appreciate the reactions I get from the apprentices, but maybe even more are the reactions I get from some "geezer" such as myself who has not been in his books for a long time. It's like revelation that "Oh yeah, I studied that 20 years ago, but NOW it makes sense". You will NEVER quit learning in this trade I don't care who you are or how hard you studied. While I usually go for the short answers in these forums, luckily we have guys like Pauluk who will take the long way home, it is what makes this the most valuable electrical forum on the net. [Linked Image]

#6226 12/29/01 05:29 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Gotta second that George......

Cindy,
well put here....job desrip or resume' material !

Quote
stay up with the [pardon me frinch] freeking codes
[Linked Image]

Page 1 of 3 1 2 3

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5