ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Whirlpool Recalls KitchenAid Electric Kettles
by Admin. 02/22/18 11:35 AM
Safest socket system for wet pottery studio?
by Jules69. 02/21/18 05:12 PM
diazed fuses
by Texas_Ranger. 02/21/18 10:22 AM
110.26
by gfretwell. 02/18/18 12:14 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
1 registered members (LongRunner), 23 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Fingersafe devices and NFPA, OSHA #61229
01/19/06 08:28 AM
01/19/06 08:28 AM
B
Bill39  Offline OP
Member
Joined: Nov 2001
Posts: 75
Indianapolis, IN, USA
A lot of the rules pertaining to working in live panels have to do with "fingersafe" devicess. But what exactly is a fingersafe device when it pertains to the NFPA and OSHA.

I believe it would be important to be able to determine immediatlely whether a device is fingersafe or not.

How big can the hole be on the terminal screwdriver... 1/8", 1/4" or what?

Work Gear for Electricians and the Trades
Re: Fingersafe devices and NFPA, OSHA #61230
01/19/06 09:29 AM
01/19/06 09:29 AM
M
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
As far as IP classification fingersafe (IP2x) is protected against objects over 12mm in diameter. Is there a NEMA equal other than calling it NEMA-1 or better?


Mike Wescoatt
Re: Fingersafe devices and NFPA, OSHA #61231
01/19/06 01:14 PM
01/19/06 01:14 PM
C
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
A few zealous inspectors (industry) carry around a "test finger" to verify that a finger can't reach any live parts.
http://www.ergonomicsusa.com/accJFP15.html

[This message has been edited by C-H (edited 01-19-2006).]

Re: Fingersafe devices and NFPA, OSHA #61232
01/19/06 03:24 PM
01/19/06 03:24 PM
M
mshaw  Offline
Member
Joined: Jan 2006
Posts: 44
Fairborn, Oh, USA
I had a test finger once but my foreman took it away, guess he did not like how I applied it

Re: Fingersafe devices and NFPA, OSHA #61233
01/19/06 06:05 PM
01/19/06 06:05 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
I don't think NFPA70E (and therefore OSHA) recognizes the term finger safe for 480V work. Table 130.2(C) says the restricted approach boundry for 480V is 1". Anything closer is considered making contact with the live part.

So finger safe terminals would help for the 50-300V "avoid contact" boundary but they would need to have a 1" recess for 480V.

NFPA79 6.2.2.1 address the dimensions and (proper) use of the "test" finger.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,052 Are you busy
181,045 Re: Forum
171,286 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.004s) Memory: 0.9671 MB (Peak: 1.1069 MB) Zlib enabled. Server Time: 2018-02-22 18:40:46 UTC