#59989 12/20/05 03:38 PM
Joined: Nov 2005
Posts: 21
O
Member
I need to run a 120V receptacle circuit and a 3/4" stub up for low voltage down a chimney space. They (the owner) say the chimney is built with double wall flue with 8-10" airspace, and then then the two courses of brick. I have no idea what the ambient temp would be in this chase. Sounds easy enough. Has anyone here ever done this? I have seen receptacles on masonary hearths but they were all new construction, never old work.

Thanks in advance.

Ty

[This message has been edited by Old Town (edited 12-20-2005).]

#59990 12/20/05 03:41 PM
Joined: Aug 2002
Posts: 1,691
S
Member
*text removed by original poster -- wrong thread*

[This message has been edited by SvenNYC (edited 12-20-2005).]

#59991 12/20/05 04:01 PM
Joined: Dec 2005
Posts: 64
J
Member
are you talking about between the flue and the brick? My guess is that it would be hot.

#59992 12/20/05 04:22 PM
Joined: Nov 2005
Posts: 21
O
Member
Yes, it will be between the flue and the brick. I am starting to wonder if I want to do this one or not. I don't think the ambient temp will really get that hot, but I am not sure.

#59993 12/20/05 04:47 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I don't think you have enough information to make an informed decision. If there is no draft stopping and ambient air can follow the conduit up the chimney space I would not expect much temperature rise but if this is only open at the top your mileage will vary, based on how much makeup air could displace the hot air that exits.
It may not get hot enough to support combustion but you have to start derating at 86f/30c.
At a combined temp (ambient plus I2R heating) of 90c/194f your THHN insulation may start failing.


Greg Fretwell
#59994 12/20/05 09:00 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I'm not sure, but it seems to me that putting anything in that air-space would violate the fire code. I think that space must be kept absolutely clear.

#59995 12/20/05 09:35 PM
Joined: Jun 2005
Posts: 821
S
Member
I have never run any type wire on the inside of a chimney.

Never.

#59996 12/20/05 11:34 PM
Joined: Nov 2005
Posts: 21
O
Member
Update:

I removed a brick above the mantle and I found this:
Behind the brick , a 2 1/2" space between the brick and sheetrock. Behind the sheetrock is an additional 8" and then a double flue setup. I can easily run flex behind the brick. What do y'all think. Thanks in advance.

Ty

#59997 12/21/05 02:45 AM
Joined: Jun 2003
Posts: 1,143
D
Member
[fallback answer] Check with your AHJ [/fallback answer]

I have no idea how hot it would get in there, but I'd consider using 90 degree C wire instead of 75.