ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 127 guests, and 22 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#59814 12/15/05 09:10 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
I received a call of lights flickering at a restaurant when the dishwasher kicks on.
What are some things to look for.
I checked for loose neutrals,hots.
They are on different circuits

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#59815 12/15/05 09:34 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Flickering as in actually going on and off a time or two, or just a momentary dip in brightness?

If the latter then it might just be the normal momentary voltage drop on the feeder caused by the switch-on surge of the motor.

#59816 12/15/05 09:46 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
a momentary dip in brightness.

#59817 12/15/05 09:47 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
Is there any way to solve this. It looks really bad when you have many people in a restautant and the lites dim every so often.

#59818 12/15/05 10:19 AM
Joined: Dec 2004
Posts: 1,064
D
Member
What type of lights, incandesant or fluro?

Dnk...

#59819 12/15/05 10:37 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
incadescent

#59820 12/15/05 01:01 PM
Joined: Dec 2003
Posts: 751
E
Member
Aside from moving the lights from phase A to phase B, or upgrading the service so that the dishwasher load won't appreciably effect the available voltage to the lights, or reducing the load to the lighting circuit by sharing the circuits, I guess the only thing is to reduce the draw on the dishwasher. Can the dishwasher be connected 240 volts? How about 3 phase?


Earl
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#59821 12/15/05 01:09 PM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
The service is new. I guess I can try and see if the manufacture has a 240v model instead

#59822 12/15/05 10:36 PM
Joined: Jun 2005
Posts: 821
S
Member
I would check and see if both circuits were on the same phase. If they are on the same phase, put one of the two on a different phase. It's worked for me before. Good luck!

#59823 12/16/05 12:00 AM
Joined: Feb 2005
Posts: 219
S
Member
If the PoCo Xfmr is shared, the loads at the neighbors house can cause the lights to flicker and dim. I the dwelling is at or near the end of the Poco ckt this can happen too. This may not be the problem but, you could be chasing ghosts.

Rob

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5