Help with an Italian overload unit #5927
12/14/01 07:58 AM
12/14/01 07:58 AM
C
ctolbert  Offline OP
Member
Joined: Aug 2001
Posts: 31
Cumming, GA USA
I have an interesting Italian overload unit that a customer is using....no brand name.

It has a little chart on the front that has the words FLC (which I assume is full load current) and Y/Delta. The vertical scale shows the current relationship to voltage on either side. I.E. Y or 460 on one side and Delta or 230 on the other side.

The issue is the dial for the overload gap is the identical scale as the Y or 460 volt FLC side.

Does the vertical scale represent the overall KVA rating of the overload?

I understood (and maybe I'm wrong) that thermal overloads were a function of material and resistivity and does not disiminate voltage sources. I.E. The unit trips at 65 amps regardless if it is 230 vac or 460 vac.

Is anyone familiar with this type of overload?

Carl

[Linked Image]

[This message has been edited by Webmaster (edited 12-14-2001).]


Carl Lee Tolbert
Technical Support
AC Drives
Automationdirect.com
Your source for the most practical automation products at almost-free pricing, delivered by 11 a.m., just by clicking a mouse.
PH: (770)844-4200
Fax:(770)886-3199
www.automationdirect.com
Work Gear for Electricians and the Trades
Re: Help with an Italian overload unit #5928
12/14/01 09:50 AM
12/14/01 09:50 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Bi-mettalic overloads trip based on current (heating) only. Voltage has nothing to do with trip settings.

I believe you are misunderstanding the meaning of the wye/delta scale. There appears to be a ratio of 1:1.77 between the left and right sides of the scale, but this is not the same as 1:2 voltage ratio you inferred. My feeling is this scale has to do with application on a wye-delta reduced voltage starter and not between normal high and low voltage motor winding connections.

Re: Help with an Italian overload unit #5929
12/14/01 12:53 PM
12/14/01 12:53 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
The right hand column numbers don't workout to the KW ratings of the corresponding FLAs.
So, that's out.
Is there any documentation? I see all sorts of labal data in the background. It should include instructions for setting the OL.
If you are concerned about setting it up, I would adjust the OL based on motor nameplate data. Remember to account for service factor.

Re: Help with an Italian overload unit #5930
12/14/01 01:20 PM
12/14/01 01:20 PM
C
ctolbert  Offline OP
Member
Joined: Aug 2001
Posts: 31
Cumming, GA USA
The label in the background is for a Cutler Hammer IEC starter that I have stickered to my test rig.

There is no documentation from the customer.

I think JBD hit it on the head. My suspicion was an additional reduced voltage starter control block option similar to the Moeller stuff I've seen.

I have tested it to the trip limits with 460 and was satisfied with the overload trigger, but I like being 100% on everything I test. I think it's odd to label something when the function is an option versus core operation.

Thanks to both of you.

Additional comments are welcome.

Carl


Carl Lee Tolbert
Technical Support
AC Drives
Automationdirect.com
Your source for the most practical automation products at almost-free pricing, delivered by 11 a.m., just by clicking a mouse.
PH: (770)844-4200
Fax:(770)886-3199
www.automationdirect.com
Re: Help with an Italian overload unit #5931
12/14/01 02:44 PM
12/14/01 02:44 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Welcome "New World Order"!
Wait until you have some poorly translated manuals. Often amusing.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
sparky 11
Trumpy 11
Popular Topics(Views)
249,261 Are you busy
187,188 Re: Forum
176,542 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.005s) Memory: 0.9690 MB (Peak: 1.1061 MB) Zlib enabled. Server Time: 2018-09-18 15:34:57 UTC