#58830 - 11/21/05 08:23 PM seu bend radius  
kdal  Offline
Member
Joined: Sep 2005
Posts: 34
Florida,U.S.A.
Hello everyone
Posted SEU meant SER
I have a few questions regarding service entrance cable.
Is it possible to come from the meter can through the wall and up without violating the bend radius. The walls are framed with 2 x 4’s.
The actual diameter of the conductors in 4/0 aluminum SE cable appears to be aprox. 5/8 to 3/4 an inch. 3/4 x 5 = 3 and 3/4 inch bending radius.
Also this puts the cable very close to the finished surface. Wouldn’t this require nail plates?
I have seen this done many times and always passed inspection. I am interested in doing things proper, not just passing inspection.



[This message has been edited by kdal (edited 11-22-2005).]


Work Gear for Electricians and the Trades

#58831 - 11/22/05 01:13 PM Re: seu bend radius  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
The only place the code requires the 1.25" setback is next to framing members.
I don't like it, or even agree but that is the way it reads and the way it gets enforced here.
A agree with your concern on service entrance conductors. I would probably go after that with 250.30(A)(1)
<service disconnect shall be>... "nearest the point of entrance of the service conductors." and tell them the "up" has to happen outside the building with the penetration right behind the service disconnect.


Greg Fretwell

#58832 - 11/22/05 01:22 PM Re: seu bend radius  
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
We have a couple of inspectors that won't allow that method on 2x4 construction walls for anything bigger than #2 ser. The minimum bending radius for Ser cable is based on the outside dimensions of the cable, not the conductors. With 4/0 cable you won't be able to make a small enough bend to meet code and stay inside the wall at the same time. See 338.24.



Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7528 MB (Peak: 0.8769 MB) Zlib enabled. Server Time: 2017-10-22 02:49:24 UTC