0 members (), 1,082 guests, and 12 robots.
#55287 08/23/05 09:45 PM
Peter Offline OP
I am installing some "Insta Hot"s and needed to know the voltage and amps.
~Peter
#55288 08/23/05 10:50 PM
Bob Offline
You need to contact the Mfg. or distributor for that information. If its residential
the voltage could be 120 or 240 volts.
#55289 08/23/05 11:29 PM
Usually your looking at 120 volt and about 10 amps, but you should check the rating on the unit in question.
#55290 08/23/05 11:39 PM
Peter Offline OP
Mr. Eagle,
Thank you for the basis. That is the problem. All I have is a set of plans and they just say "Insta Hot". I am running 12-2 MC cable.
There will be three of these on one circuit but I doubt if they would all be on at once. Or would they? This is for classrooms for a Sunday school.
I don't know the manufacturer and Google didn't help although it works good for crossword puzzles and Acrostics.
~Peter
#55291 08/24/05 12:12 AM
In most cases 1 - 12/2 per unit will get you coverd @ 120V or 240V. I would not gang them together.
Rob
#55292 08/24/05 12:28 AM
e57 Offline
"would all be on at once. Or would they?"
First start up, and every power outage or lunch time.
Heres some...
http://www.insinkerator.com/dispensers/index.shtml
The right manufacturer would be a better bet. But you'd be save to figure 120V @ 750~1800W
#55293 08/24/05 12:51 AM
You really need to get the specs on these units. I think most of the replies here are referring to the insta hot units that get installed at the kitchen sink to provide hot water for tea, etc. These units have a small tank that holds the very hot water they don’t actually heat the water instantly. If you use more than a half gallon or so of water then you will be out of hot water until the water in the tank has time to reheat. I think the units you working with are designed to instantly heat water for the faucet. They typically are 2.4 – 5.5 KW for a single sink.
http://www.eemaxinc.com/new%20spec%20sheets/SinglePoint92104.pdf
Curt Swartz
#55294 08/24/05 12:59 AM
e57 Offline
Good point!
#55295 08/24/05 03:01 AM
What this sounds like is an Electrode Boiler system.
Not unlike our "Push-through" systems here.
I'd go along with caselec with regard to the power rating, they aren't small by any means. [Linked Image]
[This message has been edited by Trumpy (edited 08-24-2005).]
#55296 08/24/05 05:14 PM
Simple answer for this. Customer must get specs or units don't get wired.