What are some examples of a "listed electrical protective system with a 1 hr fire rating" as referred to in the NEC section referenced above. Have an existing fire pump installation (not installed correctly at this time) where the AHJ will require an outside disconnecting means. Options 1 & 2 may not be practical. The fire pump controller is located about 10 foot inside the building.

Joined: May 2004
Posts: 73
R
Member
I think they mean type MI cable. I saw it for the first time last year being used for the fire pump in a nursing home. I had to trace it to the fire pump room cuz it looked like 1/2" copper tubing with orange Brady 480 v. stickers on it. It ain't cheap.

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
They went with burying the raceway in concrete on a job I inspected.


Greg Fretwell