electric pool heat pump's #51641 05/05/05 07:10 PM
Joined: Mar 2005
Posts: 42
N
northstar Offline OP
Member
does anyone have suggestions for GFCi protection on these things. at the unit or breaker. Does it matter. thanks in advance.


NORTHSTAR ELECTRIC

Work Gear for Electricians and the Trades
Re: electric pool heat pump's #51642 05/05/05 07:56 PM
Joined: Jul 2002
Posts: 8,262
Trumpy Offline
Member
northstar,
I wouldn't recommend it, these units are like a refrigeration plant and the Compressor leakage currents that are comon with this sort of equipment could trip the GFCI out.
Just to clarify that statement, I wouldn't personally fit one to any air con or refrigeration gear.
I would however use one on anything else. [Linked Image]
Hope this helps.

{Message edited to clarify statement} [Linked Image]



[This message has been edited by Trumpy (edited 05-05-2005).]

Re: electric pool heat pump's #51643 05/05/05 09:03 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Trumpy's advice has certainly stood the test of time....and, I might add, reflects upon the stormy history of the GHI- which is why I am also leery of the new AFCI mandates! But that's another thread....

For the past two years, GFI's have been manufactured to a different standard, one that supposedly reduces nuisance tripping with motor or compressor loads. Or, so they say...

It is interesting to note that there do exist GFI's, intended for use with older pool lights, that are set to trip at a higher level (20ma, I think). And AFCI's are essentially 30ma GFI's.

Now, if this is a 220v. piece of equipment, the GFI would be in the form of an expensive breaker. So would anything over 20 amps.
Best suggestion I can make is- call the heat pump maker and ask!

Re: electric pool heat pump's #51644 05/05/05 10:29 PM
Joined: Jul 2002
Posts: 8,262
Trumpy Offline
Member
Yes,
I would agree with John:
Quote
Best suggestion I can make is- call the heat pump maker and ask!

It kind of makes me wonder about the legality, or indeed the safety factor of running a piece of equipment like this, where a winding may short to ground.
This is amplified by the fact that people will be immersed in the water supplied by a unit like this.
One other recommendation I would make is ask your Inspector or AHJ about this one.
If there are GFCI's now that can overcome these Compressor leaksge currents, that would be a great leap forward.
Nuisance tripping is usually the first reason why most safety systems are either bypassed or removed completely. [Linked Image]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
258,840 Are you busy
194,361 Re: Forum
183,821 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3